Allen, 
With 8 modules in series I think I'll be looking at a Classic 250 for sure to 
be comfortable with winter morning VOC. 
I don't really know what kind of combiner situation I'll find up in the attic. 
It may be easy enough to re-wire into strings of 6 instead of strings of 8, 
though that is still probably going to push me just over the 150 VOC hard limit 
of the MX-60. I may not be able to get around replacing the controller. 

-Luke



On May 31, 2015, at 10:59 PM, Allan Sindelar <al...@sindelarsolar.com> wrote:

> Jay,
> Whoa, I'd be careful there. Unless there's been a change while I was away on 
> my bicycle, Outbacks are still 140V rated maximum voltage and 150V hard 
> maximum. 142Voc in May suggests that doubling strings in series will easily 
> exceed max Voc in winter. That's why I previously suggested Classic 200 or 
> 250. Am I missing something?
> Allan
> 
> Allan Sindelar
> al...@sindelarsolar.com
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
>  
> On 5/31/2015 2:23 PM, jay peltz wrote:
>> HI Luke,
>> 
>> To add here.  I'm unclear if you have measured each string or the whole 
>> array at 71v.  
>> I would check each string for voc/isc.  
>> 
>> And then if they are consistent, I agree that putting 2 strings in series 
>> with a new controller might help out.  
>> You can try it with the MX-60 as you are at only 142v. If it works better 
>> then a new higher voltage CC would be required for winter higher voc.
>> 
>> Let us know what you find out.
>> 
>> jay
>> 
>> 

Luke Christy

NABCEP Certified PV Installation Professionalâ„¢: Certification #031409-25 
NABCEP Certified Solar Heating Installerâ„¢: Certification #ST032611-03       
CoSEIA Certified PV Installer 

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO. 81144
sgsrenewab...@gmail.com
719.588.3044
www.sgsrenewables.com

   







_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to