I had done this a few times in the distant past, and also had done it in recent years on my own previous battery bank (four strings of S-530s - yes, I know; it was in anticipation of future plans to upgrade to 48V, and two strings wouldn't have been enough).

It worked fine - and that turned out to be a problem. I had noticed reduced capacity, but assumed foolishly that it was simply to age and cycle life (going on six years and three teenagers). Found out I had two failed cells in two different strings. The parallel connections probably - I'm not sure here - allowed the bank to perform more robustly and less obviously weakened. It might have even allowed the bank to perform as if both failed cells had been in the same string. But it also allowed me to not pay enough attention to a potentially serious problem by disguising it.

I blame myself more than the parallel connectors (just some #2 interconnects I had lying around). I'm just not sure I would use it on a customer's system.
 
Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com




On 6/1/2011 9:20 AM, toddc...@finestplanet.com wrote:

Does it make any difference to do as boB recently suggested and inter-connect the strings? So in other words, if you have two parallel strings, what happens if you parallel each battery in one string with the battery in the other string? Has anyone tried this? It might help insure more balance between each series string.

 

Todd

 

 

 

On Wednesday, June 1, 2011 3:06am, "James Surrette" <ja...@surrette.com> said:

Hi boB,


I would say maintenance is a large issue - especially when dealing with L-16's or the like, as the number of cells & connections gets large, i.e. 1000-1200AH @ 48VDC is three (3) strings, 24 batteries and 72 cells.  Will a client water 24 cells...maybe - 72??


However, from Tech Support days, imbalance is the larger problem.  It seems to take 18 months - 3 years and then you would get SG readings where one (1) bank was perfect and the other(s) is significantly lower......which is hard to overcome without effort (either break the banks & charge independently or hammer the banks and allow the high string to get even higher).


One of the key take aways that often gets overlooked is the proper initial activation of the strings.  It is impossible for all cells to have identical resting voltage.  During commissioning, each string should be charged to 2.45-2.5VPC and held until all cells read the same voltage.  If running multiple strings, then connect the strings and run the entire bank at 2.45-2.5VPC until all cells measure the same voltage.  Now the bank is well balanced and the chances of a major imbalance are greatly reduced.  However, even after this effort, if you use an amp clamp, you will notice slight differences in the amount of current being accepted by each bank.


Best,


Jamie





>>> boB Gudgel <b...@midnitesolar.com> 6/1/2011 5:00 AM >>>
On 5/31/2011 11:25 PM, Tom Elliot wrote:

Bob,

 

I totally understand the concern about multiple strings *if the strings are connected across the battery bank* as had always been the tradition in off-grid installations.  My own experience with such a bank in my system  showed why when I had a single cell get to near meltdown.  I was lucky to find it.



This might be a good reason for an installer to have one of those FLIR (or similar) thermal imager cameras.   They're a bit on the expensive side, but could
really be helpful for so many things.   Even just to know if you have left a nut loose (under load of course)

boB



Maintenance is another reason, such banks are far more difficult to maintain.  But I think those concerns are ameliorated a great deal with a buss bar installation and once I did that I never had another problem and found the battery bank much easier to maintain because the strings no longer had to be right next to each other.  Heck, it would be possible to put each series string in its own box for that matter.  And with the inclusion of string fuses that reduces problems even further.

 

When living with an off-grid system my biggest concern was system reliability and redundancy and the idea of a single string failure was a big worry which is why I never would consider it.

 

Tom

 

 

 

From: boB Gudgel

Sent: Tuesday, May 31, 2011 8:16 PM

Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

 



OK, I've been hearing for years now that one battery string is best and maybe two but no more should be used.

What is the reason for this fear ???    What is the experience with multiple strings in parallel ??

If it is because of current sharing of the strings, that shouldn't be an insurmountable problem if the wiring is done right.

If it has to do with the possibility of fire, which Darryl mentioned, seems that series string fuses could mitigate the possibility of that issue, if because of shorted cells, just like PV combiners.

Or maybe it has to do with the trouble of getting into the middle of a pile of batteries ?  Use battery boxes ?

The strings are in parallel and so they all get the same voltage, theoretically anyway if the connections are good.

I would think that the more strings, the LESS stress on individual batteries, not more.  The current in each battery should be less than it would be I would think.

So what is the real experience ??

Is a battery balancer the answer ??

Thanks,
boB






On May 31, 2011, at 8:23 PM, "Wayne Irwin" <wa...@pureenergysolar.com> wrote:

I think the verdict is 12 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) and one dry spare in storage is the best case scenario!

Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc.
State Licensed Solar Contractor
License # CVC56695

wa...@pureenergysolar.com
http://pureenergysolar.com
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

 


 


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


 


No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1375 / Virus Database: 1511/3672 - Release Date: 05/31/11

 

_______________________________________________

List sponsored by Home Power magazine


List Address: RE-wrenches@lists.re-wrenches.org


Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:

www.re-wrenches.org/etiquette.htm


Check out participant bios:

www.members.re-wrenches.org



 

This email and its attachments have been scanned by iConnection E-Mail Firewall for viruses, spam, and malicious content. The information transmitted in this email is intended only for the entity or person to which it is addressed and may contain confidential/privileged material. If you received this in error, please contact the sender and delete the material from any computer. Any review, retransmission, dissemination, or other use of this information by persons or entities other than the intended recipient is strictly prohibited. %^^%
_______________________________________________ List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to