On 5/31/2011 11:25 PM, Tom Elliot wrote:
Bob,
I totally understand the concern about multiple strings *if the
strings are connected across the battery bank* as had always been the
tradition in off-grid installations. My own experience with such a
bank in my system showed why when I had a single cell get to near
meltdown. I was lucky to find it.
This might be a good reason for an installer to have one of those FLIR
(or similar) thermal imager cameras. They're a bit on the expensive
side, but could
really be helpful for so many things. Even just to know if you have
left a nut loose (under load of course)
boB
Maintenance is another reason, such banks are far more difficult to
maintain. But I think those concerns are ameliorated a great deal
with a buss bar installation and once I did that I never had another
problem and found the battery bank much easier to maintain because the
strings no longer had to be right next to each other. Heck, it would
be possible to put each series string in its own box for that matter.
And with the inclusion of string fuses that reduces problems even
further.
When living with an off-grid system my biggest concern was system
reliability and redundancy and the idea of a single string failure was
a big worry which is why I never would consider it.
Tom
*From:* boB Gudgel <mailto:b...@midnitesolar.com>
*Sent:* Tuesday, May 31, 2011 8:16 PM
*To:* RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
*Subject:* Re: [RE-wrenches] 24 volt Battery Bank comparison
OK, I've been hearing for years now that one battery string is best
and maybe two but no more should be used.
What is the reason for this fear ??? What is the experience with
multiple strings in parallel ??
If it is because of current sharing of the strings, that shouldn't be
an insurmountable problem if the wiring is done right.
If it has to do with the possibility of fire, which Darryl mentioned,
seems that series string fuses could mitigate the possibility of that
issue, if because of shorted cells, just like PV combiners.
Or maybe it has to do with the trouble of getting into the middle of a
pile of batteries ? Use battery boxes ?
The strings are in parallel and so they all get the same voltage,
theoretically anyway if the connections are good.
I would think that the more strings, the LESS stress on individual
batteries, not more. The current in each battery should be less than
it would be I would think.
So what is the real experience ??
Is a battery balancer the answer ??
Thanks,
boB
On May 31, 2011, at 8:23 PM, "Wayne Irwin" <wa...@pureenergysolar.com
<mailto:wa...@pureenergysolar.com>> wrote:
I think the verdict is*12* - Rolls 2-YS-31 2430 AH @ 20 HR (one
string) and one dry spare in storage is the best case scenario!
Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc.
State Licensed Solar Contractor
License # CVC56695
wa...@pureenergysolar.com <mailto:wa...@pureenergysolar.com>
http://pureenergysolar.com
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell
------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
------------------------------------------------------------------------
No virus found in this message.
Checked by AVG - www.avg.com <http://www.avg.com>
Version: 10.0.1375 / Virus Database: 1511/3672 - Release Date: 05/31/11
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options& settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules& etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org