Does it make any difference to do as boB recently suggested and inter-connect 
the strings? So in other words, if you have two parallel strings, what happens 
if you parallel each battery in one string with the battery in the other 
string? Has anyone tried this? It might help insure more balance between each 
series string.
 
Todd
 
 
 
On Wednesday, June 1, 2011 3:06am, "James Surrette" <ja...@surrette.com> said:



Hi boB,

I would say maintenance is a large issue - especially when dealing with L-16's 
or the like, as the number of cells & connections gets large, i.e. 1000-1200AH 
@ 48VDC is three (3) strings, 24 batteries and 72 cells.  Will a client water 
24 cells...maybe - 72??

However, from Tech Support days, imbalance is the larger problem.  It seems to 
take 18 months - 3 years and then you would get SG readings where one (1) bank 
was perfect and the other(s) is significantly lower......which is hard to 
overcome without effort (either break the banks & charge independently or 
hammer the banks and allow the high string to get even higher). 

One of the key take aways that often gets overlooked is the proper initial 
activation of the strings.  It is impossible for all cells to have identical 
resting voltage.  During commissioning, each string should be charged to 
2.45-2.5VPC and held until all cells read the same voltage.  If running 
multiple strings, then connect the strings and run the entire bank at 
2.45-2.5VPC until all cells measure the same voltage.  Now the bank is well 
balanced and the chances of a major imbalance are greatly reduced.  However, 
even after this effort, if you use an amp clamp, you will notice slight 
differences in the amount of current being accepted by each bank.

Best,

Jamie




 >>> boB Gudgel <b...@midnitesolar.com> 6/1/2011 5:00 AM >>>
On 5/31/2011 11:25 PM, Tom Elliot wrote:



Bob,

 

I totally understand the concern about multiple strings *if the strings are 
connected across the battery bank* as had always been the tradition in off-grid 
installations.  My own experience with such a bank in my system  showed why 
when I had a single cell get to near meltdown.  I was lucky to find it.


 This might be a good reason for an installer to have one of those FLIR (or 
similar) thermal imager cameras.   They're a bit on the expensive side, but 
could
really be helpful for so many things.   Even just to know if you have left a 
nut loose (under load of course)

boB







Maintenance is another reason, such banks are far more difficult to maintain.  
But I think those concerns are ameliorated a great deal with a buss bar 
installation and once I did that I never had another problem and found the 
battery bank much easier to maintain because the strings no longer had to be 
right next to each other.  Heck, it would be possible to put each series string 
in its own box for that matter.  And with the inclusion of string fuses that 
reduces problems even further.

 

When living with an off-grid system my biggest concern was system reliability 
and redundancy and the idea of a single string failure was a big worry which is 
why I never would consider it.

 

Tom

 

 



 


From: [mailto:b...@midnitesolar.com] boB Gudgel

Sent: Tuesday, May 31, 2011 8:16 PM

To: [mailto:re-wrenches@lists.re-wrenches.org] RE-wrenches

Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

 



 OK, I've been hearing for years now that one battery string is best and maybe 
two but no more should be used.

What is the reason for this fear ???    What is the experience with multiple 
strings in parallel ??

If it is because of current sharing of the strings, that shouldn't be an 
insurmountable problem if the wiring is done right.

If it has to do with the possibility of fire, which Darryl mentioned, seems 
that series string fuses could mitigate the possibility of that issue, if 
because of shorted cells, just like PV combiners.

Or maybe it has to do with the trouble of getting into the middle of a pile of 
batteries ?  Use battery boxes ?

The strings are in parallel and so they all get the same voltage, theoretically 
anyway if the connections are good.

I would think that the more strings, the LESS stress on individual batteries, 
not more.  The current in each battery should be less than it would be I would 
think.

So what is the real experience ??

Is a battery balancer the answer ??

Thanks,
boB








 On May 31, 2011, at 8:23 PM, "Wayne Irwin" <[mailto:wa...@pureenergysolar.com] 
wa...@pureenergysolar.com> wrote:



I think the verdict is 12 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) and one 
dry spare in storage is the best case scenario!

Wayne Irwin, EEDirector of EngineeringPure Energy Solar International Inc. 
State Licensed Solar ContractorLicense # CVC56695 
[mailto:wa...@pureenergysolar.com] wa...@pureenergysolar.com
[http://pureenergysolar.com] http://pureenergysolar.com
352 377-6527 Office352 336-3299 Fax352 316-1637 Cell
 

 _______________________________________________
List sponsored by Home Power magazine

List Address: [mailto:RE-wrenches@lists.re-wrenches.org] 
RE-wrenches@lists.re-wrenches.org

Options & settings:
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
[http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
[http://www.re-wrenches.org/etiquette.htm] www.re-wrenches.org/etiquette.htm

Check out participant bios:
[http://www.members.re-wrenches.org] www.members.re-wrenches.org



 
No virus found in this message.
Checked by AVG - [http://www.avg.com] www.avg.com
Version: 10.0.1375 / Virus Database: 1511/3672 - Release Date: 05/31/11

 
_______________________________________________
List sponsored by Home Power magazine

List Address: [mailto:RE-wrenches@lists.re-wrenches.org] 
RE-wrenches@lists.re-wrenches.org

Options & settings:
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
[http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
[http://www.re-wrenches.org/etiquette.htm] www.re-wrenches.org/etiquette.htm

Check out participant bios:
[http://www.members.re-wrenches.org] www.members.re-wrenches.org


 This email and its attachments have been scanned by iConnection E-Mail 
Firewall for viruses, spam, and malicious content. The information transmitted 
in this email is intended only for the entity or person to which it is 
addressed and may contain confidential/privileged material. If you received 
this in error, please contact the sender and delete the material from any 
computer. Any review, retransmission, dissemination, or other use of this 
information by persons or entities other than the intended recipient is 
strictly prohibited. %^^%
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to