That is a good question, I have not an answer, but of course it should be based 
on the amp hour of the battery bank, absorb charging voltage, and of course the 
charging source in the case of generators.  Following Ron's advise start at C/5 
for SOC less than 50% then C/10 till about 70% SOC and then C/15 till 80% then 
C/20 to 90 %. the problem we have no way to set these values, Perhaps Ron could 
give is a routine?  The closet to SOC charging is the Outback and then the 
Magnum but both miss the goal.  

--- On Wed, 7/21/10, Dana <d...@solarwork.com> wrote:


From: Dana <d...@solarwork.com>
Subject: [RE-wrenches] RETURN AMP SETTING
To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>
Date: Wednesday, July 21, 2010, 5:54 PM

As the % of full charge is related to the of degree absorption & gravity [the 
denser & more charged acid descending, and lighter acid rising] @ what point in 
the absorption would be prudent to stop charging?

 

I used to cut off the charge on the Trace SW series at 12 “return amps”, VS. 
the factory default I think was at 5 amps.  This has & continues to work well 
but I never had anyone really answer this function clearly.

 

Is there a battery manufacturer  or wrench that would care to comment on the:  

The minimum “Return” amps to disconnect for a “full” charge?

OR

The time required per 100 AHR after reaching the Absorption point setting for 
the mix to occur?

 

I realize that battery construction, battery condition, age and temperature and 
the current power usage will also play into this factor and it may not be a 
simple answer.

 

 

 

 

 

 Dana Orzel

 

Great Solar Works, Inc

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

Responsible Technologies for Responsible People since 1988"

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, July 21, 2010 4:25 PM
To: al...@positiveenergysolar.com; 'RE-wrenches'
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters

 

Allen,

 

Can I infer that if you are shutting off the gen before charge rates drop in 
absorption that you are running only briefly in the absorb phase? Or do your 
charge currents remain high through out an extended absortion phase?

 

Perhaps you have plenty of PV which you rely upon to bring the batteries up 
through the absorption phase, once the gen is shut off.

 

I would be interest to learn more about your approach to this.

 

Thanks,

 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  

 

 

  _____  

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Wednesday, July 21, 2010 3:17 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters

The Onan RS20000 shown in the generators article in HP 131 page 98 has 
performed flawlessly as backup support to an Outback quad-stack of VFX3648s. 
Differences, however, are that this 20kW gennie charges four inverters, rather 
than two; the elevation is 6,600 feet for about a 20% output deration; there 
are no huge loads above charging draw; and the client is aware enough to shut 
it off before absorption reduces the charge rate - all different conditions 
than you have described, as the gennie is usually fully loaded and running in 
balance.

Darryl is right about the amount of words necessary.

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/> 

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3008 - Release Date: 07/21/10 
00:36:00


-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3008 - Release Date: 07/21/10 
12:36:00

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to