Mark,
Yeah, the gennie is set to come on automatically through the Mate, but the homeowner pays attention.

There's about 5kW of array for this off-grid home as well, so it's a gennie-backed PV system. Also, all modules are on trackers (long boring story) so there's plenty of PV in summer, but they depend on the generator as an integral part of charging in the winter, and the owner is involved in system operation. (He happens to be the rare customer with a Ph.D. in physics; so engaged that he successfully added a thermostatically-controlled heat exchanger with fail-safe backup to the generator's coolant lines that he piped into his solar-radiant-with-boiler infloor heating system, to increase generator overall efficiency.)

Continuous operation at low load can be harmful and inefficient, but occasional operation isn't something to lose sleep over.

Allan Sindelar
Allan@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com


On 7/21/2010 4:25 PM, Mark Frye wrote:
Allen,
 
Can I infer that if you are shutting off the gen before charge rates drop in absorption that you are running only briefly in the absorb phase? Or do your charge currents remain high through out an extended absortion phase?
 
Perhaps you have plenty of PV which you rely upon to bring the batteries up through the absorption phase, once the gen is shut off.
 
I would be interest to learn more about your approach to this.
 
Thanks,
 
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 
 


From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Wednesday, July 21, 2010 3:17 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters

The Onan RS20000 shown in the generators article in HP 131 page 98 has performed flawlessly as backup support to an Outback quad-stack of VFX3648s. Differences, however, are that this 20kW gennie charges four inverters, rather than two; the elevation is 6,600 feet for about a 20% output deration; there are no huge loads above charging draw; and the client is aware enough to shut it off before absorption reduces the charge rate - all different conditions than you have described, as the gennie is usually fully loaded and running in balance.

Darryl is right about the amount of words necessary.

Allan Sindelar
Allan@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to