I am familiar with the Myers hubs. My question was referring to the "wet-loc" connector you alluded to. Who makes those?

William Miller



At 09:00 AM 7/24/2009, you wrote:
William,

Here is a Thomas&Betts PN:

<http://www.tnb.com/ps/fulltilt/index.cgi?part=H050CP>http://www.tnb.com/ps/fulltilt/index.cgi?part=H050CP

Page 15 (A-18) of this pdf explains the hub in detail:

<http://tnblnx3.tnb.com/emAlbum/albums/tc_us/tc_1_rigidoverspec.pdf>http://tnblnx3.tnb.com/emAlbum/albums//tc_us/tc_1_rigidoverspec.pdf

-August



August Goers

Luminalt Energy Corporation
O:  415.564.7652
M:  415.559.1525
F:   650.244.9167
<http://www.luminalt.com/>www.luminalt.com
<mailto:aug...@luminalt.com>aug...@luminalt.com


----------
From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Friday, July 24, 2009 8:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] myers hubs

August:

Who manufactures these connectors?  Do you have a part number?

Marco:

Don't forget that if you do not have splices in an outdoor J box, and if your wire is wet location rated, you are not required to use Nema 3R boxes and fittings.

William Miller





At 08:27 AM 7/24/2009, you wrote:

Marco,

Interesting question. May I ask why you want to use a Myers hub rather than a standard wet-loc outdoor connector?

My understanding is that Myers hubs are used for weatherproofing and bonding (when used with a metal box) because the inside nut is serrated. See NEC 250.92(B)(2) and 314.15(A).

Anyone agree or disagree with me?

-August
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to