August:
Who manufactures these connectors? Do you have a part number?
Marco:
Don't forget that if you do not have splices in an outdoor J box, and if
your wire is wet location rated, you are not required to use Nema 3R boxes
and fittings.
William Miller
At 08:27 AM 7/24/2009, you wrote:
Marco,
Interesting question. May I ask why you want to use a Myers hub rather
than a standard wet-loc outdoor connector?
My understanding is that Myers hubs are used for weatherproofing and
bonding (when used with a metal box) because the inside nut is serrated.
See NEC 250.92(B)(2) and 314.15(A).
Anyone agree or disagree with me?
-August