August:

Who manufactures these connectors?  Do you have a part number?

Marco:

Don't forget that if you do not have splices in an outdoor J box, and if your wire is wet location rated, you are not required to use Nema 3R boxes and fittings.

William Miller





At 08:27 AM 7/24/2009, you wrote:
Marco,

Interesting question. May I ask why you want to use a Myers hub rather than a standard wet-loc outdoor connector?

My understanding is that Myers hubs are used for weatherproofing and bonding (when used with a metal box) because the inside nut is serrated. See NEC 250.92(B)(2) and 314.15(A).

Anyone agree or disagree with me?

-August

August Goers


Luminalt Energy Corporation
O:  415.564.7652
M:  415.559.1525
F:   650.244.9167
<http://www.luminalt.com/>www.luminalt.com
<mailto:aug...@luminalt.com>aug...@luminalt.com


----------
From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco
Sent: Thursday, July 23, 2009 5:36 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] myers hubs

Anyone know if Myers hubs are acceptable to use outdoors to attach to a non-metallic enclosure?

thanks,
marco