Hi Folks,

We burnt up a gen set's voltage regulator on an off-grid system sunny island/sunny boy system when we took the sunny island's off-line but didn't shut off the sunny boy. So the SB backfed the genny and fried the very expensive voltage regulator on a 30 KW system. SMA had us install a relay to tell the SB to shut down as soon as the AC reference from the SI was gone. Same situation as grid-tie really in terms of your question.

Jeff



Hi Kelly

It is an interesting issue and was just dicussing this the other day.

I think what happens if the inverter backfeeds the genny, the generator voltage will go up, if it goes up enough, it will go outside the window of the inverter and the inverter will drop out, voltage will them return to normal, inverter will reconnect and repeat.

But I sure wouldn't want to fix the generator. A relay powered from the grid will take care of the problem.

jay

peltz power
On Nov 19, 2008, at 5:24 PM, Kelly Keilwitz, Whidbey Sun & Wind wrote:

Wrenches,
I'm dredging up this subject again (previous postings 6/08) with a simple question that doesn't seem to have been answered:

Is there any issue connecting a batteryless grid-tie PV system to the load side of a panel that is backed-up by a generator on an automatic transfer switch, when the grid is down and the generator running?

In this case the PV is 5.7kW, the inverter an SMA 6000, the generator unknown size/type, but propane, automatic start, and backing up the entire main panel.

SMA tech support first said it's OK, then that the generator will blow up. I can imagine, if the inverter tries to sync with the inverter, that the voltage could rise, causing the inverter to disconnect, wait 5 minutes, repeat. Is there anything nasty that could happen?

Thanks,
-Kelly


Kelly Keilwitz, P.E.
Whidbey Sun & Wind, LLC
Renewable Energy Systems
NABCEP Certified PV Installer
987 Wanamaker Rd,
Coupeville, WA 98239
PH & FAX 360-678-7131
<>[EMAIL PROTECTED]





_______________________________________________
List sponsored by Home Power magazine

List Address: <mailto:RE-wrenches@lists.re-wrenches.org>RE-wrenches@lists.re-wrenches.org

Options & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


--
~~~~~~~~~~~~~
Jeff Clearwater
Senior Design Engineer
NABCEP (tm) Certified Solar PV Installer
http://www.nabcep.org/
Village Power Design/NorthEast Solar Design
Turnkey Solar Design & Installation for the Commercial Sector
http://www.villagepower.com
[EMAIL PROTECTED]

Voice: 413-259-3750
Fax: 413-825-0703
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to