I have been at Trane testing facility to see a live display of what can happen. That is why I am very concerned about using a T/P as a controller. The main issue is the conversion of water from liquid to vapor. Under pressure water will absorb heat but change state. As soon as the pressure is relieved by the tank splitting or a faucet turning on all of that super heated water converts from liquid to vapor in an instance the rapid expansion is the cause of the explosion.
So by building a primary control system that can open below the boiling point by using a zone valve or bi metal temp valve you can stop the pressures from happening then use the T/P as the safety to that. Again most safety device are not designed to be cycled on or off just fail at the right time. A while ago at Trane they would test 5000 high temperature limit switches to see if they would fail at 180 degrees +- but out all of the test they never checked the same switch twice. But control switches are cycled thousands of times. Chris Meier Product Manager UniRac, Inc. 1411 Broadway Blvd. NE Albuquerque, NM 87102-1545 Ph: 505-242-6411 Fx: 505-242-6412 Email: [EMAIL PROTECTED] Web: http://www.unirac.com This message contains confidential and privileged information, which is intended for the individual(s) to whom it is addressed. It should not be reviewed, retransmitted, disseminated, or otherwise used by a person(s) or entities other than the intended recipient. If you received this message in error, please contact the sender and delete the material from your computer system(s). -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of jay peltz Sent: Wednesday, November 12, 2008 9:35 AM To: RE-wrenches Subject: Re: [RE-wrenches] Pt valves as overheat control Hi Chris, Here is the mythbusters video. http://www.youtube.com/watch?v=JmJoyuUJj2Q jay peltz power On Nov 12, 2008, at 8:00 AM, Chris Meier wrote: > Please do not forget any safety device in HVAC or plumbing is > not designed to cycle open and close as a controller. They are > designed > to fail and in a lot cases they are designed to fail once. After the > T/P > opens it may never really reset which is ok because it will leak but > the > P/T could also loss the calibration which means they can stay closed > even if they should be open. In many cases this means the house is > leveled when the explosion happens. > > > > Chris Meier > > Product Manager > > UniRac, Inc. > > 1411 Broadway Blvd. NE > > Albuquerque, NM 87102-1545 > > Ph: 505-242-6411 > > Fx: 505-242-6412 > > Email: [EMAIL PROTECTED] > > Web: http://www.unirac.com > _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org