Drake,
690.64 relates everything to the service disconnects. All the rest of this is semantics. As long as the PV connection is upstream of the service disconnect (i.e. in between the service disconnect and the service meter), it is considered a line side service connection. If there is no way to turn off the residential service in the panel with the "feed-thru" lugs, there is no service disconnect for the residential service yet. That way if the connection were on the line side of the first service disconnect for the residence (one of two services at the site, both coming from the same service drop-to get all the semantics proper), it is considered a line-side connection. So what is it..? Bill. From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Drake Chamberlin Sent: Thursday, July 31, 2008 9:13 AM To: RE-wrenches Subject: Re: [RE-wrenches] Gray code area At 03:24 PM 7/30/2008, you wrote: According to the two paragraphs above, the commercial building has two commercial services??? One will receive PV and one will not?? One service is for the commercial building and one is for the residence. There is one service drop to two meters. Both services will be fed PV. Drake Chamberlin Athens Electric OH License 44810 CO License 3773 740-448-7328 303-328-5533
_______________________________________________ List sponsored by Home Power magazine RE-wrenches@lists.re-wrenches.org http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out participant bios: www.mrsharkey.com/wrenches/