Drake:

Sorry again, but this is still not clear. Questions below in red (could you draft a block diagram and post it?):

At 03:56 PM 7/30/2008, Drake Chamberlin wrote:

2. The commercial building has a service that you will not feed the grid-tie to.

Yes. It also has its own service. The commercial building gets some solar also. The tax benefits would be for it all to be on the commercial service, but we are following the owner's request.

According to the two paragraphs above, the commercial building has two commercial services??? One will receive PV and one will not??


3. This commercial building has a "feed-through" breaker panel that was installed for the PV to tie to. This "Feed-through" box does not connect to the commercial service.

Yes

Where is the service that the PV system would feed?  In a separate building?

Yes, in the residence on the property. The meter is on the commercial building.

Referring to the passage above: I have learned that in most cases, the service and the meter are the same device. Are you telling me the legal service is separate from the meter???


Where does the feeder connected to the bottom of this "Feed-through" panel go?



It goes to the residence, which is another building on the same property.
_______________________________________________
List sponsored by Home Power magazine

RE-wrenches@lists.re-wrenches.org

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Reply via email to