Bruce Klawiter wrote:
>>> Well I hope it is solved and I don't even know how I did it.
>>>       
>> OHHHhhh NOOooooo!  That's the worst kind, as it can come BACK!
>>     
> I know, I spent the rest of the day trying to get the twitching to come 
> back so I would know what the problem was, but I can't.
>
>   
It is almost impossible to make a bad connector go flaky on demand.  Any
messing with it generally cleans the contact plating and makes it stay good
for a while.
>> Well, this is NOT OK!  .1 V AC on the minus power supply to the op 
>> amps in the servo amp is a real problem.  And, it isn't your meter, 
>> as the + side is reading .001, which is fine.
>>     
>
> Well then I will have to find a new power supply.
>   
Or just replace the bulk filter cap for the minus side.  it ought to be 
easy to
locate these caps, they should be the biggest ones in the supply.
>   
>> Yes, the DAC outputs have a signal pin and a ground pin.  
>> The encoder board also has a ground pin for each encoder.
>>     
> With only the encoders plugged into the PPMC boards the D-sub 
> connector does not show ground. 
>   
Right, in many units the encoder is totally isolated from machine frame
for best noise immunity.
> OK let make sure I am saying this right with only the encoder 
> plugged in and my meter set to ohms, one lead on the D-sub 
> connector and on on the chassis it shows an open circuit. If I plug 
> in the amp to the DAC or the parallel cable my meter shows a dead short.
> Not that this helps of changes anything I just want to make sure I
> am explaining it rigth
>
> Would there be any benefit to moving all the grounds to one one point, this 
> would be fairly easy to do.
>   
Since it is now working, I would be very afraid to change the ground 
arrangement,
as it could cause a ground loop situation.  If you are positive you can 
put it back if
it causes a problem, then you can try it.  But, Anilam may have spent 
considerable
time putting the ground system the way it works best.  You have no way 
to know
about that.

Jon

------------------------------------------------------------------------------
All the data continuously generated in your IT infrastructure contains a
definitive record of customers, application performance, security
threats, fraudulent activity and more. Splunk takes this data and makes
sense of it. Business sense. IT sense. Common sense.
http://p.sf.net/sfu/splunk-d2d-oct
_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to