I am working on an internal document showing examples of the voltage Rating
for products that have different power sources.

Currently, our North American 3-phase devices are rated 230V 3~, and our EU
versions are rated 400V 3~.  But in the future, we may wish to use the
Neutral to which the Rating becomes more complicated.

Thanks for the input.
The Other Brian

On Wed, Apr 9, 2025 at 7:10 PM Ralph McDiarmid <rmm.priv...@gmail.com>
wrote:

> 230/400V 3~ is nominal voltage for the EU and widely used in low-voltage
> distribution, and the USA uses 277/480V common in industrial, and 120/208V
> for commercial.
>
>
>
> Ralph
>
>
>
> *From:* John Woodgate <j...@woodjohn.uk>
> *Sent:* April 9, 2025 1:13 PM
> *To:* EMC-PSTC@LISTSERV.IEEE.ORG
> *Subject:* Re: [PSES] Fwd: Rating Label Nomenclature
>
>
>
> Hi, Brian. You don't say whether the product is for Europe or the
> Americas, or elsewhere. By the voltages, It's Europe, but it's best to be
> clear.  In principle, the Product Standard is definitive, so what does it
> say? I have never seen the PE mentioned in this context, and it's best to
> keep the information as simple as is sufficient. I doubt that the order of
> the voltage and supply type statements is critical.
>
> Does the product need a neutral? If not, don't mention it; use 400V 3~
> unless the Product Standard requires something different.
>
> On 2025-04-09 20:55, Brian Kunde wrote:
>
> I am reading through IEC 61293:2020 and comparing it to what some of the
> Product Standards say and examples on the Web regarding the Voltage Rating
> that would go on a Nameplate or Label.  I am really struggling with 3 phase
> voltage ratings. Industrial machines show this information as a table, but
> we want to just have a single line Rating.  Our equipment is not a
> transformer or motor driven device, but it is powered by 3-phase.  Let me
> know if this is correct or if there is a better way.  Thank you.
>
> The Other Brian
>
>
>
> Single Phase = 230V~
>
> Three Phase (no neutral) = 400V 3~      or should it be 3~400V
>
> Three Phase with neutral = 230/400V 3/N~      or should it be 3/N~230/400V
>
>
>
> Is the PE conductor assumed or should it be included in the Rating, as in
> these examples?
>
> Three Phase without neutral and PE = 400V 3/PE~     or 3/PE~230/400V
>
> Three Phase with neutral and PE = 230/400V 3/N/PE~     or 3/N/PE~230/400V
>
>
>
> For a Three Phase device that uses the Neutral, do you always show the
> Phase Voltage in addition to the Line Voltage, or it is assumed?
>
> Does the "3~" go after the voltage or before?  The  IEC 61293:2020 shows
> it before, but I generally see it after.
>
>
>
>
> ------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to
> EMC-PSTC@LISTSERV.IEEE.ORG
>
> All emc-pstc postings are archived and searchable on the web at:
> https://www.mail-archive.com/emc-pstc@listserv.ieee.org/
> <https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>
>
> Website: https://ewh.ieee.org/soc/pses/
> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
> List rules:
> https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
>
> For help, send mail to the list administrators:
> Mike Sherman at: msherma...@comcast.net
> Rick Linford at: linf...@ieee.org
>
> For policy questions, send mail to:
> Jim Bacher at: j.bac...@ieee.org
> ------------------------------
>
> To unsubscribe from the EMC-PSTC list, click the following link:
> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
>
> --
> Best wishes John Woodgate RAYLEIGH Essex OOO-Own Opinions Only
> www.woodjohn.uk If something is true: * as far as we know - it's science
> *for certain - it's mathematics *unquestionably - it's religion
>
>
>
>
> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>
> Virus-free.www.avg.com
> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
> ------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to
> EMC-PSTC@LISTSERV.IEEE.ORG
>
> All emc-pstc postings are archived and searchable on the web at:
> https://www.mail-archive.com/emc-pstc@listserv.ieee.org/
> <https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>
>
> Website: https://ewh.ieee.org/soc/pses/
> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
> List rules:
> https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
>
> For help, send mail to the list administrators:
> Mike Sherman at: msherma...@comcast.net
> Rick Linford at: linf...@ieee.org
>
> For policy questions, send mail to:
> Jim Bacher at: j.bac...@ieee.org
> ------------------------------
>
> To unsubscribe from the EMC-PSTC list, click the following link:
> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
> ------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to
> EMC-PSTC@LISTSERV.IEEE.ORG
> All emc-pstc postings are archived and searchable on the web at:
> https://www.mail-archive.com/emc-pstc@listserv.ieee.org/
>
> Website: https://ewh.ieee.org/soc/pses/
> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
> List rules:
> https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
>
> For help, send mail to the list administrators:
> Mike Sherman at: msherma...@comcast.net
> Rick Linford at: linf...@ieee.org
>
> For policy questions, send mail to:
> Jim Bacher at: j.bac...@ieee.org
> ------------------------------
>
> To unsubscribe from the EMC-PSTC list, click the following link:
> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to