For anyone “skilled in the art”, it would be hard to misconstrue “ 230/400V “ 
as anything other that a mains connection requiring four current-carrying 
conductors.  (a “Y” connection as some would say)   Phase rotation might be 
important too, and so a symbol to instruct the installer to consult the product 
documentation should also be on the nameplate.
 
From: Bansi Patel <bansipate...@gmail.com> 
Sent: April 9, 2025 9:04 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Fwd: Rating Label Nomenclature
 
277/480 V in L-N/L-L (phase to neutral / phase to phase). It could be single 
phase or three phase.
 
Best Regards and Be Safe

Bansi Patel
BRP Consultants
IEEE PSES Emeritus (2025-2027)
IEEE PSES, Board of Governors-at Large (2018-2023, 2025-2027)
IEEE PSES San Dirgo Chapter Chair 2020-2025
IEEE San Diego Section ExCom, Member At Large 2025 
IEEE PSES San Diego Chapter chair 2025 
 <mailto:bansipate...@gmail.com> bansipate...@gmail.com
M:  <tel:909-260-9403> 909-260-9403
Please plan to attend the Face-to-Face event:
ISPCE 2025, (May 13-15, 2025), San Francisco, California, USA
 <https://2025.psessymposium.org/> https://2025.psessymposium.org/
 
From: Ralph McDiarmid <rmm.priv...@gmail.com <mailto:rmm.priv...@gmail.com> > 
Sent: Wednesday, April 9, 2025 4:10 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Subject: Re: [PSES] Fwd: Rating Label Nomenclature
 
230/400V 3~ is nominal voltage for the EU and widely used in low-voltage 
distribution, and the USA uses 277/480V common in industrial, and 120/208V for 
commercial.  
 
Ralph
 
From: John Woodgate <j...@woodjohn.uk <mailto:j...@woodjohn.uk> > 
Sent: April 9, 2025 1:13 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> 
Subject: Re: [PSES] Fwd: Rating Label Nomenclature
 
Hi, Brian. You don't say whether the product is for Europe or the Americas, or 
elsewhere. By the voltages, It's Europe, but it's best to be clear.  In 
principle, the Product Standard is definitive, so what does it say? I have 
never seen the PE mentioned in this context, and it's best to keep the 
information as simple as is sufficient. I doubt that the order of the voltage 
and supply type statements is critical.
Does the product need a neutral? If not, don't mention it; use 400V 3~   unless 
the Product Standard requires something different.
On 2025-04-09 20:55, Brian Kunde wrote:
I am reading through IEC 61293:2020 and comparing it to what some of the 
Product Standards say and examples on the Web regarding the Voltage Rating that 
would go on a Nameplate or Label.  I am really struggling with 3 phase voltage 
ratings. Industrial machines show this information as a table, but we want to 
just have a single line Rating.  Our equipment is not a transformer or motor 
driven device, but it is powered by 3-phase.  Let me know if this is correct or 
if there is a better way.  Thank you. 
The Other Brian
 
Single Phase = 230V~
Three Phase (no neutral) = 400V 3~      or should it be 3~400V
Three Phase with neutral = 230/400V 3/N~      or should it be 3/N~230/400V
 
Is the PE conductor assumed or should it be included in the Rating, as in these 
examples?  
Three Phase without neutral and PE = 400V 3/PE~     or 3/PE~230/400V
Three Phase with neutral and PE = 230/400V 3/N/PE~     or 3/N/PE~230/400V
 
For a Three Phase device that uses the Neutral, do you always show the Phase 
Voltage in addition to the Line Voltage, or it is assumed?  
Does the "3~" go after the voltage or before?  The  IEC 61293:2020 shows it 
before, but I generally see it after.  
 
 

  _____  

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>  
All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
<https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>  
Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf 
For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net <mailto:msherma...@comcast.net> 
Rick Linford at: linf...@ieee.org <mailto:linf...@ieee.org>  
For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org <mailto:j.bac...@ieee.org>  

  _____  

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 
-- 
Best wishes John Woodgate RAYLEIGH Essex OOO-Own Opinions Only www.woodjohn.uk 
<http://www.woodjohn.uk>  If something is true: * as far as we know - it's 
science *for certain - it's mathematics *unquestionably - it's religion
 

 
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 
Virus-free. 
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 www.avg.com
  _____  

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>  
All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
<https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>  
Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf 
For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net <mailto:msherma...@comcast.net> 
Rick Linford at: linf...@ieee.org <mailto:linf...@ieee.org>  
For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org <mailto:j.bac...@ieee.org>  
  _____  

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 
  _____  

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>  
All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
<https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>  
Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf 
For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net <mailto:msherma...@comcast.net> 
Rick Linford at: linf...@ieee.org <mailto:linf...@ieee.org>  
For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org <mailto:j.bac...@ieee.org>  
  _____  

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 
  _____  

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>  
All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
<https://www.mail-archive.com/emc-pstc@listserv.ieee.org/%20>  
Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf 
For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net <mailto:msherma...@comcast.net> 
Rick Linford at: linf...@ieee.org <mailto:linf...@ieee.org>  
For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org <mailto:j.bac...@ieee.org>  
  _____  

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: 
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to