Volt-amperes (VA) would be sufficient since active power (W) cannot be greater 
than VA.  (recall the power triangle)

I’d rather use “power” not “active power”, since “active” doesn’t add anything 
to the definition of that term.

 

I would avoid ambiguity such as, “…ports of significant burden  “

 

And, 125 V is a poor example because it is not a nominal voltage in North 
America.  It’s 120 V or 120/240 V or 120/208 V – those are common nominal 
values found in low-voltage distribution for residential and commercial 
buildings in North America.

 

 

Ralph

 

From: Boštjan Glavič <[email protected]> 
Sent: Thursday, August 22, 2024 9:51 PM
To: '[email protected]' <[email protected]>; [email protected]
Subject: RE: [PSES] Burden test

 

Thank you all. I decided to contact TC57 which prepared this standard and let’s 
see.

 

When I went once more through standard, I think it is really like apparent 
power. So it shall be equal to power consumption of power supply under normal 
load.

 

Below extract from standard – clauses with word Burden.

 

Best regards,

Boštjan

 

5.4 Rated burden

The burden for the power supply (a.c. including power factor/d.c.) at quiescent 
state and

maximum load.

The maximum start-up inrush current of the power supply circuits shall also be 
stated.

 

 

 

6.1.3 Auxiliary supplies, I/O

6.1.3.1 General requirements for marking

For marking the following should be taken into account:

• a.c. – with symbol 2 of Table 3 and rated frequency or frequency range;

• d.c. – with symbol 1 of Table 3;

• symbol 3 of Table 3 on equipment for a.c. and d.c. supply;

• a hyphen (-) shall be used to separate the lower and upper nominal voltages, 
for example,

125 V-230 V;

• the burden in watts (active power) or volt-amperes (apparent power) or the 
rated input

current, with all accessories or plug-in modules connected.

The documentation shall specify the burden of individual digital inputs, output 
relays and

other I/O ports of significant burden in order for the user to calculate the 
worst-case

burden for the equipment application.

The values shall be measured with the equipment powered at nominal voltage, but 
not be

operational.

The measured value shall not exceed the marked value by more than 10 %;

 

 

6.1.3.2 Auxiliary supply

The following information shall be provided on the equipment and in the 
documentation:

• a.c. and/or d.c. supply;

• the rated values.

• in the documentation:

• the burden.

6.1.3.3 Inputs

The following information shall be provided in the documentation:

• a.c. and/or d.c. supply;

• the rated values;

• burden on the supply input.

 

6.1.3.4 Outputs

The following information shall be provided in the documentation:

• the kind of output, for example, relay, optocoupler etc;

• burden on the supply input;

• the switching capability on/off;

• the switching voltage;

• the permissible current, continuous value and short time value for 1 s;

• withstand voltage across open contacts.

Compliance with 6.1.3.1 to 6.1.3.4 is checked by inspection or by measurement.

 

6.8 Burden test

Burden 6.8.1 for AC power supply

6.8.1.1 Typical load condition

The equipment is powered at rated auxiliary energizing voltage with typical 
load of all input

and outputs. The test shall be carried out by voltamperes (VA) measurement. The 
maximum

value of 5 consecutive tests shall be used for burden claim.

6.8.1.2 Inrush current and power-up duration

The equipment is switched on at rated auxiliary energizing voltage. The peak 
value of input

current during power-up, the duration from switching instant to the instant 
that input current

gets to within 10 % of quiescent state current shall be recorded. The maximum 
value of

5 consecutive tests shall be used for inrush current and power-up duration 
claim.

From: Ralph McDiarmid <[email protected] <mailto:[email protected]> > 
Sent: Thursday, August 22, 2024 9:23 PM
To: [email protected] <mailto:[email protected]> 
Subject: Re: [PSES] Burden test

 


CAUTION: This email originated from outside of our organisation. Do not click 
links or open attachments unless you recognise the sender and know the content 
is safe.

 

I agree with John’s comment.  I will add that standard writing panels 
(committees) should use their vocabulary with intelligence.  Any ambiguous 
terms should be defined somewhere in part one of IEC 61850.  I don’t have a 
copy, and the IEC preview doesn’t help.

 

I will hazard a guess that in this context, the adjective “intelligent” means a 
power supply that is able to communication over a network for the exchange of 
data and for remote control or configuration.

 

Ralph

 

From: John Woodgate <[email protected] <mailto:[email protected]> > 
Sent: Thursday, August 22, 2024 10:41 AM
To: [email protected] <mailto:[email protected]> 
Subject: Re: [PSES] Burden test

 

I think you are required to state the power consumption of every port that 
consumes power. If your SMPS really is 'intelligent', then the standard 
applies. But I wonder what the relevant definition of 'intelligent' is. There 
appears to be no method of measurement for IQ!

On 2024-08-22 17:53, Richard Nute wrote:

 

Hi Bostjan:

 

While this does not answer your specific questions, it may be helpful:

 

https://en.wikipedia.org/wiki/IEC_61850

 

Good luck, and best regards,

Rich

 

 

From: Boštjan Glavič  <mailto:[email protected]> 
<[email protected]> 
Sent: Thursday, August 22, 2024 4:32 AM
To: [email protected] <mailto:[email protected]> 
Subject: [PSES] Burden test

 

Dear all,

 

Is anyone familiar with burden test according IEC 61850-3 standard? Is this 
test applicable for switch mode  power supply with AC input and DC output?

 

How to conduct the test? What is the idea of the test?

 

Standard is not really clear.

 

Thank you for your support.

 

Best regards,

Bostjan

 

 


  _____  


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected] <mailto:[email protected]>  

All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/[email protected]/ 
<https://www.mail-archive.com/[email protected]/%20>  

Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: [email protected] <mailto:[email protected]> 
Rick Linford at: [email protected] <mailto:[email protected]>  

For policy questions, send mail to:
Jim Bacher at: [email protected] <mailto:[email protected]>  


  _____  


To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 

-- 
OOO - Own Opinions Only
Best Wishes
John Woodgate
Keep trying

 


 
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 

Virus-free. 
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 www.avg.com

  _____  

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected] <mailto:[email protected]>  

All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/[email protected]/ 
<https://www.mail-archive.com/[email protected]/%20>  

Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: [email protected] <mailto:[email protected]> 
Rick Linford at: [email protected] <mailto:[email protected]>  

For policy questions, send mail to:
Jim Bacher at: [email protected] <mailto:[email protected]>  

  _____  

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 

  _____  

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected] <mailto:[email protected]>  

All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/[email protected]/ 
<https://www.mail-archive.com/[email protected]/%20>  

Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: [email protected] <mailto:[email protected]> 
Rick Linford at: [email protected] <mailto:[email protected]>  

For policy questions, send mail to:
Jim Bacher at: [email protected] <mailto:[email protected]>  

  _____  

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC 
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to