I set mine to low when I install them due to that same post I've seen over
the years.

Josh Luthman
24/7 Help Desk: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373


On Mon, Sep 21, 2020 at 11:00 AM Larry Smith <lesm...@ecsis.net> wrote:

> We had to set the sensitivity (sp?) setting on all our APC
> UPS to medium (drop from default of HIGH) or they would
> not accept the generator current (would stay on battery).
>
> --
> Larry Smith
> lesm...@ecsis.net
>
> On Mon September 21 2020 09:43, Ken Hohhof wrote:
> > 110v at the generator or the other end of the 175 feet of 10 AWG wire?
> >
> >
> >
> > And total load is 5-6 amps each including the UPS charging the
> batteries?
> > What kind of UPS?  Something like an APC will have a relatively low
> > charging current, other setups may be quite a bit higher.  I know our
> Alpha
> > UPS units have programmable charging current and I had to lower it in
> case
> > the only generator I have available is our smallest Honda 1000 VA,
> > otherwise the generator would run for a minute or two and then trip on
> > overload.
> >
> >
> >
> > Doing the math on voltage drop in the wire, 10 AWG is around 1 ohm per
> 1000
> > feet, and you have 350 feet of wire including hot and neutral.  So 0.35
> ohm
> > times 5.5 amps is 2 volts.  Assuming the generator is putting out 120
> > volts, that wouldn’t account for a 10 volt drop.
> >
> >
> >
> > Sounds like you suspect the generator can’t handle the load and as a
> result
> > is putting out low voltage.
> >
> >
> >
> > What kind of generator is this?  Is it an inverter style?  What is the VA
> > rating?  If it’s just a standard generator for power tools and stuff, a
> UPS
> > will sometimes find the voltage or frequency out of spec or unstable and
> > refuse to run off it.  If it’s just an APC UPS or something like that,
> > sometimes they have a sensitivity setting that you can set lower.
> >
> >
> >
> >
> >
> > From: AF <af-boun...@af.afmug.com> On Behalf Of Josh Luthman
> > Sent: Monday, September 21, 2020 9:22 AM
> > To: AFMUG <af@af.afmug.com>
> > Subject: [AFMUG] Generator power supply questions
> >
> >
> >
> > So Friday we have another 3 phase go down in the building.  They
> unplugged
> > it all so that wing had nothing.
> >
> >
> >
> > As a precaution I start up the generator.  When they're cutting the other
> > phases we are using I move it to the generator.  The generator complains
> > and the UPS units don't switch over.  I drop it to say 90% open choke and
> > the UPS switches over - but it's only 110v.  I'd like to know what's
> going
> > on here.
> >
> >
> >
> > I have 175 feet of 10 gauge (times 2).  Two circuits on the generator,
> two
> > runs of copper, two UPS.  UPS is doing about 5-6 amps each.
> >
> >
> > What can I do better?  Should I?  It runs but I'd like to keep it as
> simple
> > as possible to avoid "teaching someone" to lower it from full open choke.
> >
> >
> >
> > Josh Luthman
> > 24/7 Help Desk: 937-552-2340
> > Direct: 937-552-2343
> > 1100 Wayne St
> > Suite 1337
> > Troy, OH 45373
>
> --
> AF mailing list
> AF@af.afmug.com
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to