110v at the generator or the other end of the 175 feet of 10 AWG wire?

 

And total load is 5-6 amps each including the UPS charging the batteries?  What 
kind of UPS?  Something like an APC will have a relatively low charging 
current, other setups may be quite a bit higher.  I know our Alpha UPS units 
have programmable charging current and I had to lower it in case the only 
generator I have available is our smallest Honda 1000 VA, otherwise the 
generator would run for a minute or two and then trip on overload.

 

Doing the math on voltage drop in the wire, 10 AWG is around 1 ohm per 1000 
feet, and you have 350 feet of wire including hot and neutral.  So 0.35 ohm 
times 5.5 amps is 2 volts.  Assuming the generator is putting out 120 volts, 
that wouldn’t account for a 10 volt drop.

 

Sounds like you suspect the generator can’t handle the load and as a result is 
putting out low voltage.

 

What kind of generator is this?  Is it an inverter style?  What is the VA 
rating?  If it’s just a standard generator for power tools and stuff, a UPS 
will sometimes find the voltage or frequency out of spec or unstable and refuse 
to run off it.  If it’s just an APC UPS or something like that, sometimes they 
have a sensitivity setting that you can set lower.

 

 

From: AF <af-boun...@af.afmug.com> On Behalf Of Josh Luthman
Sent: Monday, September 21, 2020 9:22 AM
To: AFMUG <af@af.afmug.com>
Subject: [AFMUG] Generator power supply questions

 

So Friday we have another 3 phase go down in the building.  They unplugged it 
all so that wing had nothing.

 

As a precaution I start up the generator.  When they're cutting the other 
phases we are using I move it to the generator.  The generator complains and 
the UPS units don't switch over.  I drop it to say 90% open choke and the UPS 
switches over - but it's only 110v.  I'd like to know what's going on here.

 

I have 175 feet of 10 gauge (times 2).  Two circuits on the generator, two runs 
of copper, two UPS.  UPS is doing about 5-6 amps each.


What can I do better?  Should I?  It runs but I'd like to keep it as simple as 
possible to avoid "teaching someone" to lower it from full open choke.

 

Josh Luthman
24/7 Help Desk: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to