Before the UPS units were plugged in, it ran just fine.  Once they were
plugged in it sounded like it was struggling/running out of gas - this was
resolved by closing the choke a little bit.  Do you think that's a
frequency problem?

110vac at the UPS.  I didn't measure what was coming out of the generator.

6 amps per UPS load.  It charges very slowly so maybe 7-8 amps.  Still,
well within the 20 amp circuit limit.  Generator has a 220v 30 amp plug as
well.  It's an 8500w unit.  This is it:
https://www.lowes.com/pd/Troy-Bilt-6250-8500-Watt-Gasoline-Portable-Generator-with-Briggs-Stratton-Engine/4732729

UPS is two 1500va APC- Smart UPS 1500VA.  It's an OLDER version of this:
https://www.amazon.com/APC-Smart-UPS-SMX1500RM2U-1500VA-System/dp/B002TIR2Z2/

Josh Luthman
24/7 Help Desk: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373


On Mon, Sep 21, 2020 at 10:44 AM Ken Hohhof <af...@kwisp.com> wrote:

> 110v at the generator or the other end of the 175 feet of 10 AWG wire?
>
>
>
> And total load is 5-6 amps each including the UPS charging the batteries?
> What kind of UPS?  Something like an APC will have a relatively low
> charging current, other setups may be quite a bit higher.  I know our Alpha
> UPS units have programmable charging current and I had to lower it in case
> the only generator I have available is our smallest Honda 1000 VA,
> otherwise the generator would run for a minute or two and then trip on
> overload.
>
>
>
> Doing the math on voltage drop in the wire, 10 AWG is around 1 ohm per
> 1000 feet, and you have 350 feet of wire including hot and neutral.  So
> 0.35 ohm times 5.5 amps is 2 volts.  Assuming the generator is putting out
> 120 volts, that wouldn’t account for a 10 volt drop.
>
>
>
> Sounds like you suspect the generator can’t handle the load and as a
> result is putting out low voltage.
>
>
>
> What kind of generator is this?  Is it an inverter style?  What is the VA
> rating?  If it’s just a standard generator for power tools and stuff, a UPS
> will sometimes find the voltage or frequency out of spec or unstable and
> refuse to run off it.  If it’s just an APC UPS or something like that,
> sometimes they have a sensitivity setting that you can set lower.
>
>
>
>
>
> *From:* AF <af-boun...@af.afmug.com> *On Behalf Of *Josh Luthman
> *Sent:* Monday, September 21, 2020 9:22 AM
> *To:* AFMUG <af@af.afmug.com>
> *Subject:* [AFMUG] Generator power supply questions
>
>
>
> So Friday we have another 3 phase go down in the building.  They unplugged
> it all so that wing had nothing.
>
>
>
> As a precaution I start up the generator.  When they're cutting the other
> phases we are using I move it to the generator.  The generator complains
> and the UPS units don't switch over.  I drop it to say 90% open choke and
> the UPS switches over - but it's only 110v.  I'd like to know what's going
> on here.
>
>
>
> I have 175 feet of 10 gauge (times 2).  Two circuits on the generator, two
> runs of copper, two UPS.  UPS is doing about 5-6 amps each.
>
>
> What can I do better?  Should I?  It runs but I'd like to keep it as
> simple as possible to avoid "teaching someone" to lower it from full open
> choke.
>
>
>
> Josh Luthman
> 24/7 Help Desk: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
> --
> AF mailing list
> AF@af.afmug.com
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to