Unless you can justify separate fire areas, you are stuck with the full 1500
 
 
 
 
Todd Williams    

 
Fire Protection Design/Consulting
 
Stonington, CT
 
860-608-4559
 
 
 
 
 

 
 
>  
> On Apr 30, 2026 at 10:30 AM,  <Matt Grise (mailto:[email protected])>  
> wrote:
>  
>  
>  
>  
>
> I am looking at a building that has a 16' ceiling in MOST areas. There is a 
> small 250sf entry vestibule that has a 24' ceiling. The vestibule is 
> separated from the interior by walls and doors, but they are not fire rated 
> (so it would not meet separation requirements for a Room Design approach per 
> 13, 2016 ed 11.2.3.3). The vestibule has sprinklers at its high ceiling level.
>
>  
>
>  
>
>  
>
> Is the unrated wall enough of a separation (draft curtain) between the 
> ceiling levels to allow for a QR reduction in the area/density calc for the 
> main floor? Would it be required to use a 1500sf operating area under the 
> vestibule without regard   to the walls?
>
>  
>
>  
>
>  
>
>  Thanks!
>
>  
>
>  
>
>  
>