Even though they aren’t “officially” rated walls generally speaking any drywall wall is going to meet the 30 minutes for light hazard, the opening protective maybe doesn’t, but in that case you can move down to exception 2 and calculate a couple heads in the communicating space, which drops you to like 4 heads, and probably becomes a less demanding area than a reduced remote area elsewhere and can be ignored. That would be my thought anyway.
Mike Morey 2025 NFSA Top Tech Champion<https://www.linkedin.com/posts/national-fire-sprinkler-association_congratulations-to-our-2025-top-tech-winner-activity-7326725245707431936-_5jg/> • NICET IV<https://credentials.nicet.org/47458792-752e-4926-86fc-bd4d47722218#acc.kBTieRXy> • CFPS<https://www.credly.com/badges/c05de73a-dbed-4c31-b1dc-0be93f3151f0/public_url> Project Estimator • Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive • Fort Wayne, IN • 46825 direct 260.487.7824 / cell 260.417.0625 email [email protected]<mailto:[email protected]> 24/7<outlook-data-detector://2/> SERVICE LINE 888.217.7055<tel:888.217.7055> [cid:[email protected]] From: Matt Grise <[email protected]> Sent: Thursday, April 30, 2026 10:30 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] QR area reduction - area separation I am looking at a building that has a 16' ceiling in MOST areas. There is a small 250sf entry vestibule that has a 24' ceiling. The vestibule is separated from the interior by walls and doors, but they are not fire rated (so it would ZjQcmQRYFpfptBannerStart This Message Is From an Untrusted Sender You have not previously corresponded with this sender. ZjQcmQRYFpfptBannerEnd I am looking at a building that has a 16' ceiling in MOST areas. There is a small 250sf entry vestibule that has a 24' ceiling. The vestibule is separated from the interior by walls and doors, but they are not fire rated (so it would not meet separation requirements for a Room Design approach per 13, 2016 ed 11.2.3.3). The vestibule has sprinklers at its high ceiling level. Is the unrated wall enough of a separation (draft curtain) between the ceiling levels to allow for a QR reduction in the area/density calc for the main floor? Would it be required to use a 1500sf operating area under the vestibule without regard to the walls? Thanks! Matt Grise This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient.
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]