Thanks for the responses.  One last question on the matter.  I was also asked 
if they could store the plastic commodities up to the acceptable height on the 
racks and then put additional Class I-IV commodities above them up to their 
allowable height.  Is this allowed?  I thought I read somewhere that is wasn't 
but can't find it now.

Thank you,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]]

From: Dewayne Martinez <[email protected]>
Sent: Wednesday, June 4, 2025 9:15 AM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: Open top containers

I have a customer that would like to store group A non-expanded plastic in 
racks.  The majority of the product will be completely enclosed in a cardboard 
box but some of them will be in a cardboard box but with no top.
Am I right to consider the ones with no top as an "open-top" container and must 
be stored only on the lowest level of the racks?  Would these now be considered 
exposed non-expanded plastic.  I was thinking no because the packaging 
surrounding the commodity will absorb water and retard the burning hazard of 
the commodity.

Thank you,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to