Dewayne,

My understanding is that an "open top" container prevents water from being distributed as it should be, limiting where the water is supposed to flow. 

Consider - the fire begins six feet away from an open top carton as you've described.  The sprinkler above activates and begins to discharge water, only the water is captured by the container and does not disburse as intended.

I hope that is of some help,
Ken Wagoner, SET
Parsley Consulting
3002 Younger Drive
Harrisonville, Missouri 64701-3909

Phone: (760) 745-6181
Visit the website
Please note new street address


On 6/4/2025 9:15 AM, Dewayne Martinez wrote:

I have a customer that would like to store group A non-expanded plastic in racks.  The majority of the product will be completely enclosed in a cardboard box but some of them will be in a cardboard box but with no top.

Am I right to consider the ones with no top as an “open-top” container and must be stored only on the lowest level of the racks?  Would these now be considered exposed non-expanded plastic.  I was thinking no because the packaging surrounding the commodity will absorb water and retard the burning hazard of the commodity.  

 

Thank you,

 

Dewayne Martinez

Fire Protection Design Manager

 

TOTAL Mechanical

Building Integrity


W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected]

Ph:  262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/ 

          

 


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to