I can't believe it was FM's intention to allow, say, a 47" duct to be located 
directly below the sprinkler and within only a few inches of the deflector. But 
I am having a hard time finding where something is written to refute that.

If it was NFPA 13, I think we'd be saying that it needs to be a minimum of 18" 
below the deflector before we apply that allowance to allow the pattern to 
develop.

Kyle Montgomery
 [cid:[email protected]]
Pre-Construction Manager
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



From: Ed van Riel <[email protected]>
Sent: Thursday, April 3, 2025 12:07 AM
To: [email protected]
Subject: [External][Sprinklerforum] FM Global obstruction

You don't often get email from 
[email protected]<mailto:[email protected]>. Learn why this is 
important<https://aka.ms/LearnAboutSenderIdentification>
Here below is a passage from FM 2.0 (2021-10) non-storage.
(2.5.2.5.4.1 Any object up to 4 ft (1.2 m) wide, as measured in the object's 
least dimension and in a plane
that is parallel to the floor, does not qualify as an obstruction to the 
sprinkler's discharge pattern.)

Is anything up to 4ft. wide no obstruction? no matter what the vertical 
distance from the deflector (or themal element) is?
Or do we have to respect the clearance of 3 ft (0.9 m)?