I believe 4’ wide applies to objects more than 3’ below the sprinkler, objects 
above that have to comply with either the three times rule or the checkerboard 
pattern figures that precede that section (analogous to the NFPA objects near 
the sprinkler tables eg distance to edge vs distance allowed below deflector).


Mike Morey

CFPS 3229 • NICET S.E.T. 123677

Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company

7614 Opportunity Drive • Fort Wayne, IN • 46825

direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]

[Image]

________________________________
From: Ed van Riel <[email protected]>
Sent: Thursday, April 3, 2025 3:06:50 AM
To: [email protected] 
<[email protected]>
Subject: [Sprinklerforum] FM Global obstruction

Here below is a passage from FM 2. 0 (2021-10) non-storage. (2. 5. 2. 5. 4. 1 
Any object up to 4 ft (1. 2 m) wide, as measured in the object’s least 
dimension and in a plane that is parallel to the floor, does not qualify as an 
obstruction to the sprinkler’s
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.

ZjQcmQRYFpfptBannerEnd
Here below is a passage from FM 2.0 (2021-10) non-storage.
(2.5.2.5.4.1 Any object up to 4 ft (1.2 m) wide, as measured in the object’s 
least dimension and in a plane
that is parallel to the floor, does not qualify as an obstruction to the 
sprinkler’s discharge pattern.)

Is anything up to 4ft. wide no obstruction? no matter what the vertical 
distance from the deflector (or themal element) is?
Or do we have to respect the clearance of 3 ft (0.9 m)?


This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to