Andre,

I agree with Mike Watts on accelerators as many just don’t understand them or 
how they work.  Why back in the day when we would install an accelerator we 
would keep the manufacturers spec sheet as they always towards the back had a 
trouble shooting section and also a maintenance section that was very helpful 
to see how to tear them down to clean.  But also too many are just in a hurry 
and don’t clean them out correctly or make sure to wait and remove all the 
water so it doesn’t build up.  Another thing that I used to do was make sure 
the accelerator did set up 100%.  I would disconnect the discharge side and 
take a cup of water and hold it over the discharge pipe as sometimes in valve 
rooms it was super loud and I could hold the cup of water and see if any air 
bubbles were coming out.  That way I was sure it was set up 100% or was leaking 
by a little and I needed to clean it out better.  Too many are in a hurry and 
accelerators should be put back in service or documented on their inspection 
report as to why and told to the customer.

Matt Bass, CFPS  |   Technical Program Manager AMZL-GSF-AGL, Fire Protection & 
Life Safety |
Global Reliability Team  |  WNC6 – North Carolina, USA
E: [email protected]<mailto:[email protected]>    Wiki: Fire and Life 
Safety<https://w.amazon.com/bin/view/BaseBuildingManagement/Fire_Life_Safety/#H5ProjectsandPreventive2FCorrectiveActions>
   Slack:  #fire-life-safety-help
[cid:[email protected]]

From: Mike Watts <[email protected]>
Sent: Thursday, February 20, 2025 10:48 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Dry valve actuator


CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you can confirm the sender and know the 
content is safe.


A lot of times You will find an accelerator valved out and that is totally 
wrong. The accelerator is there because the system volume.  The time it takes 
to get the water to the outlet in the event of a fire. The accelerator is 
looking for a 3psi drop in pressure, and it will activate the the system, 
making a trip faster. Most of them put air pressure on the intermediate 
chamber, which changes the surface area ratio of the valve and makes the valve 
open to get water to the fire within the amount of time for the hazard of the 
area.

Most of the time, the accelerator is not the problem. It is something to do 
with the air supply. Lots of techs are afraid of them because they don't 
understand them, so they just leave them off. If I recall right nfpa states, 
they should be monitored i totally agree with monitoring them.



Mike Watts
Sprinkler Service Manager
Firetrol Protection Systems
4616 W. Howard Lane, Suite 700
Austin, TX. 78728
512-687-0115 Office
512‐660-4411 Cell
[email protected]<mailto:[email protected]>

________________________________
From: Mike Watts <[email protected]<mailto:[email protected]>>
Sent: Thursday, February 20, 2025 9:42:59 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: Re: [Sprinklerforum] Dry valve actuator

Are you talking about an accelerator?

Mike Watts
Sprinkler Service Manager
Firetrol Protection Systems
4616 W. Howard Lane, Suite 700
Austin, TX. 78728
512-687-0115 Office
512‐660-4411 Cell
[email protected]<mailto:[email protected]>

________________________________
From: Andre smilz <[email protected]<mailto:[email protected]>>
Sent: Thursday, February 20, 2025 9:04:20 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Dry valve actuator

What is the purpose of an actuator on a dry valve I've come across so many out 
of service are they really that difficult to clean out and put back in service? 
Having a hard time finding info on how to clean them out and put back in 
service. 
What is the purpose of an actuator on a dry valve I've come across so many out 
of service are they really that difficult to clean out and put back in service? 
Having a hard time finding info on how to clean them out and put back in 
service.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to