The actuator controls the opening of the dry pipe valve, the accelerator speeds 
up the process of dumping air to get to the trip point.

The actuator also releases air but in a different way than the accelerator does.


Jeff Brickell, CET
Senior Estimator/Designer
NICET III CERTIFIED
CERT #147245

OREGON CERTIFIED COBID FIRM #13272
(EMERGING SMALL BUSINESS)

TRIAD FIRE PROTECTION
[cid:[email protected]]
OREGON . WASHINGTON . ARIZONA

OFFICE  503.856.6333
CELL       602.550.4292
FAX        866.766.8862

From: Mike Watts <[email protected]>
Sent: Thursday, February 20, 2025 8:48 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Dry valve actuator

A lot of times You will find an accelerator valved out and that is totally 
wrong. The accelerator is there because the system volume.  The time it takes 
to get the water to the outlet in the event of a fire. The accelerator is 
looking for a 3psi drop in pressure, and it will activate the the system, 
making a trip faster. Most of them put air pressure on the intermediate 
chamber, which changes the surface area ratio of the valve and makes the valve 
open to get water to the fire within the amount of time for the hazard of the 
area.

Most of the time, the accelerator is not the problem. It is something to do 
with the air supply. Lots of techs are afraid of them because they don't 
understand them, so they just leave them off. If I recall right nfpa states, 
they should be monitored i totally agree with monitoring them.



Mike Watts
Sprinkler Service Manager
Firetrol Protection Systems
4616 W. Howard Lane, Suite 700
Austin, TX. 78728
512-687-0115 Office
512‐660-4411 Cell
[email protected]<mailto:[email protected]>

________________________________
From: Mike Watts <[email protected]<mailto:[email protected]>>
Sent: Thursday, February 20, 2025 9:42:59 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: Re: [Sprinklerforum] Dry valve actuator

Are you talking about an accelerator?

Mike Watts
Sprinkler Service Manager
Firetrol Protection Systems
4616 W. Howard Lane, Suite 700
Austin, TX. 78728
512-687-0115 Office
512‐660-4411 Cell
[email protected]<mailto:[email protected]>

________________________________
From: Andre smilz <[email protected]<mailto:[email protected]>>
Sent: Thursday, February 20, 2025 9:04:20 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Dry valve actuator

What is the purpose of an actuator on a dry valve I've come across so many out 
of service are they really that difficult to clean out and put back in service? 
Having a hard time finding info on how to clean them out and put back in 
service. 
What is the purpose of an actuator on a dry valve I've come across so many out 
of service are they really that difficult to clean out and put back in service? 
Having a hard time finding info on how to clean them out and put back in 
service.
_________________________________________________________