Thanks for the answers, I'd already come to the same conclusion just
second guessing.
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 2/14/2025 12:53 PM, Greg McGahan wrote:
Yes
Greg McGahan
Genesis Fire Services, LLC.
------------------------------------------------------------------------
*From:* Bob Knight <[email protected]>
*Sent:* Friday, February 14, 2025 11:31 AM
*To:* [email protected]
<[email protected]>
*Subject:* [Sprinklerforum] Sloped Ceilings
NFPA 13 (2019 ED) 19.3.3.2.4 Sloped Ceilings requires a 30% increase
in design area when the roof slope exceeds 2 in 12. I have always
thought that this was for quick response sprinklers. I've actually
never had a situation where QR weren't being used, so I haven't given
this any thought before. Now I have a non storage project with a 3 in
12 roof slope using standard response sprinklers, OH2.
Is the 30% increase required for both quick and standard response
sprinklers?
--
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
Virus-free.www.avg.com
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
--
This email has been checked for viruses by AVG antivirus software.
www.avg.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]