Thanks for the answers, I'd already come to the same conclusion just second guessing.

/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 2/14/2025 12:53 PM, Greg McGahan wrote:
Yes


Greg McGahan

Genesis Fire Services, LLC.



------------------------------------------------------------------------
*From:* Bob Knight <[email protected]>
*Sent:* Friday, February 14, 2025 11:31 AM
*To:* [email protected] <[email protected]>
*Subject:* [Sprinklerforum] Sloped Ceilings
NFPA 13 (2019 ED) 19.3.3.2.4 Sloped Ceilings requires a 30% increase in design area when the roof slope exceeds 2 in 12.  I have always thought that this was for quick response sprinklers.  I've actually never had a situation where QR weren't being used, so I haven't given this any thought before.  Now I have a non storage project with a 3 in 12 roof slope using standard response sprinklers, OH2. Is the 30% increase required for both quick and standard response sprinklers?
--

/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT

<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> Virus-free.www.avg.com <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]


--
This email has been checked for viruses by AVG antivirus software.
www.avg.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to