| Yes - absolutely. Thanks, John John August Denhardt, P.E Vice President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 Are you a member with a technical question? Don't forget one of the most valuable resources that AFSA provides is Technical Reviews by our Technical Services Department. It’s like having an FPE on your staff. Visit www.firesprinkler.org/
NFPA 13 (2019 ED) 19.3.3.2.4 Sloped
Ceilings requires a 30% increase in design area when the roof
slope exceeds 2 in 12. I have always thought that this was for
quick response sprinklers. I've actually never had a situation
where QR weren't being used, so I haven't given this any thought
before. Now I have a non storage project with a 3 in 12 roof
slope using standard response sprinklers, OH2. Is the 30% increase required for both quick and standard response sprinklers? --
Thank you,
Bob Knight, CET III Fire by Knight, LLC 208-318-3057 <FBK-LOGO-EMAIL.jpg> _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected] |