I have found that piping the discharge back to the tank allows for a discharge nozzle with pitot to be inside the tank and right at the manhole cover, this satisfies the requirement to have a secondary means of testing other than a meter in a bypass loop. There is then no need to run a line out to the building edge and then running multiple hoses for each flow test. This saves time and money on each 3rd year fire pump full flow test. I have done this on many projects, and it is a much less expensive option. Most jurisdictions here in Washington state only require discharge water to be treated if it will run outside into the storm drains thus piping back to the tank alleviates this requirement since the water will be captured and not run outside.
Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:[email protected]] From: Ken Wagoner <[email protected]> Sent: Wednesday, September 25, 2024 6:55 AM To: [email protected] Subject: [Sprinklerforum] Re: Water tank return line Having worked most of my career on the 'left' coast, I can confirm Ryan's remarks, In one jurisdiction there was a requirement that discharge from a fire pump had to be captured, treated, and returned to the reservoir after the testing confirmed that the water was 'clean.' As you may imagine the already high cost of a fire pump was increased by this requirement. sincerely, Ken Wagoner, SET Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri 64701-2235 Phone: (760) 745-6181 Visit the website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1> On 9/25/2024 8:43 AM, Hinson, Ryan wrote: Not per NFPA 20. It is provided as an option. Certain jurisdictions such as on the Left coast may have requirements to minimize water wastage. I’ll let them chime further. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Associate Fire Protection Engineer \ Upper Midwest Region O 612-900-3755 \ M 763-688-4045 \ F 952-229-2923 [email protected]<mailto:[email protected]> \ burnsmcd.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fburnsmcd.com&c=E,1,TKRybk-ff3FFLHP8XEtafZtQLkAOsEV9PK0dfLDFZX82bjhL88Z8PGNCbFGwek8iqLWvqmFKcdRVIABedmdm2s8DS2An6lrQf7DwbvQtTw7X6L0,&typo=1&ancr_add=1> 8201 Norman Center Drive, Suite 500 \ Bloomington, MN 55437 *Registered in: AK, LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems Layout From: Tim Easter <[email protected]><mailto:[email protected]> Sent: Wednesday, September 25, 2024 8:39 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]><mailto:[email protected]> Subject: [Sprinklerforum] Re: Water tank return line I understand it's allowed, but is it required? Thank you. On Wed, Sep 25, 2024, 9:16 AM Hinson, Ryan <[email protected]<mailto:[email protected]>> wrote: Return to source or return to reservoir is specifically allowed both for test header- and pressure relief valve discharge per NFPA 20 (2022) Sections 4.20.6, 4.20.7, and 4.20.8 with appropriate provisions. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Associate Fire Protection Engineer \ Upper Midwest Region O 612-900-3755 \ M 763-688-4045 \ F 952-229-2923 [email protected]<mailto:[email protected]> \ burnsmcd.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fburnsmcd.com&c=E,1,H0YXby7ne40l_Roxuc3tg6Z_hEcmrS0tgcvscyBA5E9Uf9tMesPfScNODUzXChEbKZ1ztR4xgvaCqj9dOPr85pLsY9MZv36s197TYVVOHjHa0_mu-FWx&typo=1&ancr_add=1> 8201 Norman Center Drive, Suite 500<https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g> \<https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g> Bloomington, MN 55437<https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g> *Registered in: AK, LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems Layout From: Tim Easter <[email protected]<mailto:[email protected]>> Sent: Wednesday, September 25, 2024 5:42 AM To: [email protected]<mailto:[email protected]> Subject: [Sprinklerforum] Water tank return line Is there a code requirement to return discharge of the fire pumps to the water tank? _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,INaxPqDMhnikREmDusG0krmLnIcgPxqF1JUsHyGl_UsWNqvPjU6i4dQfw4PI2iUF0Thr7ogtWXWWEa0i3r3vSg4WKRhQHYuVsNcYHwae&typo=1&ancr_add=1> To unsubscribe send an email to [email protected]<mailto:[email protected]> _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,EpEJlY5RuVB2l6mpw5rfL_cdbVfFdWRyeHdunl0M8BW6qe890LqgMS7GB2kJljkfveya_A8aagvzzbbfZWyBG44YVvn4thIad74e7J6fYpNmBHi8933EZfZzdg,,&typo=1&ancr_add=1> To unsubscribe send an email to [email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]