I have found that piping the discharge back to the tank allows for a discharge 
nozzle with pitot to be inside the tank and right at the manhole cover, this 
satisfies the requirement to have a secondary means of testing other than a 
meter in a bypass loop. There is then no need to run a line out to the building 
edge and then running multiple hoses for each flow test. This saves time and 
money on each 3rd year fire pump full flow test.
 I have done this on many projects, and it is a much less expensive option.  
Most jurisdictions here in Washington state only require discharge water to be 
treated if it will run outside into the storm drains thus piping back to the 
tank alleviates this requirement since the water will be captured and not run 
outside.


Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]




From: Ken Wagoner <[email protected]>
Sent: Wednesday, September 25, 2024 6:55 AM
To: [email protected]
Subject: [Sprinklerforum] Re: Water tank return line

Having worked most of my career on the 'left' coast, I can confirm Ryan's 
remarks,

In one jurisdiction there was a requirement that discharge from a fire pump had 
to be captured, treated, and returned to the reservoir after the testing 
confirmed that the water was 'clean.'

As you may imagine the already high cost of a fire pump was increased by this 
requirement.

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>



On 9/25/2024 8:43 AM, Hinson, Ryan wrote:
Not per NFPA 20.  It is provided as an option.  Certain jurisdictions such as 
on the Left coast may have requirements to minimize water wastage.  I’ll let 
them chime further.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer \ Upper Midwest Region
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fburnsmcd.com&c=E,1,TKRybk-ff3FFLHP8XEtafZtQLkAOsEV9PK0dfLDFZX82bjhL88Z8PGNCbFGwek8iqLWvqmFKcdRVIABedmdm2s8DS2An6lrQf7DwbvQtTw7X6L0,&typo=1&ancr_add=1>
8201 Norman Center Drive, Suite 500  \  Bloomington, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Tim Easter <[email protected]><mailto:[email protected]>
Sent: Wednesday, September 25, 2024 8:39 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]><mailto:[email protected]>
Subject: [Sprinklerforum] Re: Water tank return line

I understand it's allowed, but is it required? Thank you.

On Wed, Sep 25, 2024, 9:16 AM Hinson, Ryan 
<[email protected]<mailto:[email protected]>> wrote:
Return to source or return to reservoir is specifically allowed both for test 
header- and pressure relief valve discharge per NFPA 20 (2022) Sections 4.20.6, 
4.20.7, and 4.20.8 with appropriate provisions.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer \ Upper Midwest Region
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fburnsmcd.com&c=E,1,H0YXby7ne40l_Roxuc3tg6Z_hEcmrS0tgcvscyBA5E9Uf9tMesPfScNODUzXChEbKZ1ztR4xgvaCqj9dOPr85pLsY9MZv36s197TYVVOHjHa0_mu-FWx&typo=1&ancr_add=1>
8201 Norman Center Drive, Suite 
500<https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g>
  
\<https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g>
  Bloomington, MN 
55437<https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g>
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Tim Easter <[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 25, 2024 5:42 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Water tank return line


Is there a  code requirement to return discharge of the fire pumps to the water 
tank?


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,INaxPqDMhnikREmDusG0krmLnIcgPxqF1JUsHyGl_UsWNqvPjU6i4dQfw4PI2iUF0Thr7ogtWXWWEa0i3r3vSg4WKRhQHYuVsNcYHwae&typo=1&ancr_add=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>





_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,EpEJlY5RuVB2l6mpw5rfL_cdbVfFdWRyeHdunl0M8BW6qe890LqgMS7GB2kJljkfveya_A8aagvzzbbfZWyBG44YVvn4thIad74e7J6fYpNmBHi8933EZfZzdg,,&typo=1&ancr_add=1>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to