I understand it's allowed, but is it required? Thank you.

On Wed, Sep 25, 2024, 9:16 AM Hinson, Ryan <[email protected]> wrote:

> Return to source or return to reservoir is specifically allowed both for
> test header- and pressure relief valve discharge per NFPA 20 (2022)
> Sections 4.20.6, 4.20.7, and 4.20.8 with appropriate provisions.
>
>
>
> *Ryan L. Hinson**, PE*, SET***  \  Burns & McDonnell
>
> Associate Fire Protection Engineer \ Upper Midwest Region
>
> *O* 612-900-3755 \  *M* 763-688-4045 \  *F* 952-229-2923
>
> *[email protected] <[email protected]>*  \  burnsmcd.com
> <http://www.burnsmcd.com/>
>
> 8201 Norman Center Drive, Suite 500
> <https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g>
> \
> <https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g>
> Bloomington, MN 55437
> <https://www.google.com/maps/search/8201+Norman+Center+Drive,+Suite+500+%5C+Bloomington,+MN+55437?entry=gmail&source=g>
>
> *Registered in: AK, LA, MD, MN, PA, TX, & UT
>
> **NICET IV - Water-Based Systems Layout
>
>
>
> *From:* Tim Easter <[email protected]>
> *Sent:* Wednesday, September 25, 2024 5:42 AM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] Water tank return line
>
>
>
>
> Is there a  code requirement to return discharge of the fire pumps to the
> water tank?
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to