Tom, good to hear you are still out there.   
  

  
There are a lot of variables (like how long they do each flow, etc) that will 
impact how much water is saved or used. I don’t think there is enough 
consistency to make it viable. You would have to pick a time of flow and meter 
the exact flow rate.   
  

  
You also need to realize that the test is to evaluate if the pump is running at 
capacity and not to give you numbers for design.   
  

  
The most restrictive place I have been to for discharge is the Coast Guard 
Academy in New London,CT. You can’t discharge on grass and only in to certain 
drains. This is more of a problem for relief valves as both pumps have flow 
meters going back into the suction. I’m not sure is these restrictions are true 
at other military facilities because I haven’t been on other bases for work in 
a while.   
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Sep 3, 2024 at 7:00 PM,  <Tduross1 (mailto:[email protected])>  wrote:
>   
>   
>         
>   
>   
>   
> >   
> >   
> >
> > I’m looking for backup, for a claim I base, but can’t back up.
> >
> >   
> >
> > I’m wondering if anyone here has ever done a green points calculation for 
> > the benefit of having a flow meter on a fire pump and rat racing back to 
> > suction rather than waste.    I’ve heard many talking of this and how 
> > conscious they are in our effort to save water but I’m wondering if anyone 
> > has ever submitted applications, calculated savings, or presented evidence. 
> >    I’d also be interested in local or regional purveyor requirements on 
> > waste, reclamation and disposal.
> >
> >   
> >
> > Go Red Sox.
> >
> >   
> >
> >   
> >
> >   
> >
> > Tom Duross
> >
> >   
> >   
>   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to