Brian, Looks like you're quoting one I did about a month ago. Don't forget that with a roof slope of > 4 in 12 and if sprinklers installed where the dimension Perpendicular to the slope exceeds 8'-0" shall have a minimum pressure of 20PSI. I try to avoid that much pressure required and space my heads 8'-0" on center.
Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:[email protected]] From: Brian Harris <[email protected]> Sent: Wednesday, August 28, 2024 5:42 AM To: [email protected] Subject: [Sprinklerforum] Interstitial or Attic Quoting a wood framed building with a flat roof in the center. First thought was interstitial heads under it but then got to thinking, since there's not another floor above wouldn't attic or upright heads be acceptable instead. I guess I'm wondering if having a floor above is what drives interstitial heads? [cid:[email protected]] Thank you, Brian Harris, CET BVS Systems Inc. bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fbvssystemsinc.com&c=E,1,fNefe4uv2J-NRwNaysFp2KsoNrciaKwaRQlCj-2liiOz8y_dBZG1Pc_uVTUVRt86qsbe8Po-FQVxQ86JSh9hGLM6aqSZPECCgRgI4y6-9jbqH1MSgrE,&typo=1&ancr_add=1> Phone: 704.896.9989 Fax: 704.896.1935