Don't forget that with a roof slope of > 4 in 12 and if sprinklers installed 
where the dimension Perpendicular to the slope exceeds 8'-0" shall have a 
minimum pressure of 20PSI. I try to avoid that much pressure required and space 
my heads 8'-0" on center.

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]




From: Brian Harris <[email protected]>
Sent: Wednesday, August 28, 2024 5:42 AM
To: [email protected]
Subject: [Sprinklerforum] Interstitial or Attic

Quoting a wood framed building with a flat roof in the center. First thought 
was interstitial heads under it but then got to thinking, since there's not 
another floor above wouldn't attic or upright heads be acceptable instead. I 
guess I'm wondering if having a floor above is what drives interstitial heads?