It is important not to just throw around the word "attic".

An attic is a combustible concealed space, members less than 3 on center, with 
a pitch of 4/12 or greater.

There is no distinction on occupancy above for interstitial.

A combustible concealed space, less than 2/12, and less than 36" deep.

R/
Matt

Matthew J. Willis, CWBSP, C.E.T.
Ferguson Fire Design, LLC
D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249>
[email protected]<mailto:[email protected]>

From: Brian Harris <[email protected]>
Sent: Wednesday, August 28, 2024 6:42 AM
To: [email protected]
Subject: [Sprinklerforum] Interstitial or Attic

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Quoting a wood framed building with a flat roof in the center. First thought 
was interstitial heads under it but then got to thinking, since there's not 
another floor above wouldn't attic or upright heads be acceptable instead. I 
guess I'm wondering if having a floor above is what drives interstitial heads?

[cid:[email protected]]

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to