We are supposed to label them as such. 5.2.5.2 in the 23 edition of 25

Benjamin Young


On Tue, Jul 30, 2024 at 11:09 AM Fpdcdesign <[email protected]> wrote:

> One of the things that I see, living in an area with 80+ year old systems,
> is that the newer inspectors are asking for calc signs on pipe schedule
> systems. Hydraulically calculating  pipe schedule system can be a disaster.
> They are 2 separate and individual system designs. A system may not
> necessarily meet both sets of criteria.
>
> A good example is a school in my town that has a pipe schedule system
> installed in the 1950s. I was asked to do a hydraulic calculation. The 2535
> sqft design area in the attic contained 54 sprinklers. No way that calc was
> going to work.
>
> We probably should be labeling pipe schedule systems as such.
>
> Todd Williams
> Fire Protection Design/Consulting
> Stonington, CT
> 860-608-4559
>
>
> On Jul 30, 2024 at 10:56 AM, <Ken Wagoner <[email protected]>>
> wrote:
>
> There is certainly an issue on that missing information.  NFPA 25
> addresses the need for this sign/information in §5.2.5 (2023 ed). And some
> of the "enhanced content" on NFPA Link to this section that this is to be
> noted as a "deficiency", although it is a "noncritical" deficiency as it
> doesn't impair the ability of the system to function in a fire.
>
> I've done considerable work on existing buildings which were being
> repurposed from a factory to storage, and without this information the
> costs of the revisions went way up since a retro set of calculations had to
> be performed.
>
> just my thoughts,
> *Ken Wagoner, SET*
>
>
> *Parsley Consulting 500 West Mechanic Street
> <https://www.google.com/maps/search/500+West+Mechanic+Street+%0D%0A++++++++++Harrisonville,+Missouri+64701-2235?entry=gmail&source=g>
> Harrisonville, Missouri 64701-2235
> <https://www.google.com/maps/search/500+West+Mechanic+Street+%0D%0A++++++++++Harrisonville,+Missouri+64701-2235?entry=gmail&source=g>*
> *Phone: (760) 745-6181 *
> *Visit the website
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
>
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to