Thanks for the background and clarification Steve, I appreciate it.

Jamie Seidl NICET SET #107472
Century Fire Protection<http://www.centuryfp.com/> | General Manager
3600 Woodpark Blvd. Suite G Charlotte, NC 28206
PLEASE NOTE NEW ADDRESS
____________________________________________________________________
p  704 888 3473 |  m  704 650 0033

From: Steve Leyton <[email protected]>
Sent: Wednesday, July 3, 2024 11:36 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: 2013 NFPA 14 7.5.3

External Email: ONLY open links/attachments from known safe sources
Damn you guys - I'm not on vacation and was awake when Rick pinged as well.   
This may come as a shock but we need our morning coffee and time to make 
breakfast and #2 on the West Coast same as y'all.

As they say, if you're using an older edition of a standard  want to confirm or 
clarify the committee's intent on a particular issue, look at the most current 
edition of that standard.   Moving from 2013 to 2016, there was a subtle change 
in 7.5.3 where it was revised to say, "Where wet standpipes are 
interconnected...", so that clarifies the intent that it be applied to wet 
only.  There's also 7.5.4 that states, "Dry standpipes shall have only a single 
level of interconnection", so looping a dry manual was taken off the table.

Jump ahead to 2024 and (renumbered) 9.4 has been simplified.   9.4.3 still 
restricts dry standpipes to a single interconnection but overall, you can 
interconnect at any level (unless the system is supplied by a rooftop tank), no 
check valves are required, and with the AHJ's approval standpipes don't need to 
be interconnected at all.

When the committee opened discussion of the check valve requirement this past 
cycle, we couldn't figure out why that was even in the standard.   It's been 
there for so long that it became inertial at some point, I guess.   I/we have 
gone over this quite a bit and, so long as there are sectional valves that 
enable isolation of a standpipe, we couldn't figure out why a check was 
required.

But I'm also concerned about looping manual standpipes because if there's a 
hydraulic advantage but the system has to be sectionally isolated, then a 
dead-end calc' should be the basis of design.   I'm a proponent of the KISS 
theory.  (When Caputo and I were advocating and lobbying city building and fire 
officials for residential fire sprinklers back in the 80's he used to say that 
the best and simplest residential sprinkler system was just pipe, fittings and 
sprinklers and no extraneous valves or connections.    I agree with that 
approach, especially with manual standpipes.)    There are scenarios with 
multi-zone systems where interconnection to supply a higher zone is one of the 
approved arrangements, but if I'm the AHJ, I'm down with a single 
interconnection and no check valves, wet or dry.

SL
Bright eyed and bushy tailed, whatever that's supposed to mean



From: Jamie Seidl <[email protected]<mailto:[email protected]>>
Sent: Wednesday, July 03, 2024 5:44 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] FW: 2013 NFPA 14 7.5.3

Quick question on a holiday week.
7.5.3 states that "Where standpipes are interconnected at the top and bottom, 
check valves shall be installed at the base of each standpipe to prevent 
circulation".
Is this requirement intended to apply to manual dry standpipes?  NFPA 14 does 
not appear to make a distinction in this case, but if they're intended to 
prevent circulation, I would imagine that is not a concern with a manual dry 
system.
Steve, are you on vacation yet?  This one is up your alley.

Thanks for your time.

Jamie Seidl NICET SET #107472
Century Fire Protection<http://www.centuryfp.com/> | General Manager
3600 Woodpark Blvd. Suite G Charlotte, NC 28206
___________________________________________________________________
p  704 888 3473 |  m  704 650 0033 Facebook<https://www.facebook.com/CenturyFP> 
  LinkedIn<https://www.linkedin.com/company/century-fire-protection>   
Twitter<https://twitter.com/centuryfp>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to