It’s too early on the west coast so Steve is probably asleep. 😀

I don’t have the standard so I don’t know what it says and I don’t understand 
the need for the check valves at the base. 

However, if the standpipes are interconnected at the top, then I think there 
should be a control valve in that connection at top to allow sectioning off 
each standpipe separately from the other one if any repair work needs to be 
done on it. This would apply to both wet and manual systems. 
Just my opinion. 
Rick Matsuda 

> On Jul 3, 2024, at 7:45 AM, Jamie Seidl <[email protected]> wrote:
> 
> 
> Quick question on a holiday week.
> 7.5.3 states that "Where standpipes are interconnected at the top and bottom, 
> check valves shall be installed at the base of each standpipe to prevent 
> circulation”.
> Is this requirement intended to apply to manual dry standpipes?  NFPA 14 does 
> not appear to make a distinction in this case, but if they're intended to 
> prevent circulation, I would imagine that is not a concern with a manual dry 
> system.
> Steve, are you on vacation yet?  This one is up your alley.
>  
> Thanks for your time.
>  
> Jamie Seidl NICET SET #107472
> Century Fire Protection | General Manager
> 3600 Woodpark Blvd. Suite G Charlotte, NC 28206
> ___________________________________________________________________
> 
> p  704 888 3473 |  m  704 650 0033 Facebook   LinkedIn   Twitter
>  
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to