7.5.4 Dry standpipes shall have only a single level of interconnection. You can't interconnect on both the top and bottom of dry standpipes.
Thomas R. Worley Estimator/Design Manager Fire Foe Corp. 999 Trumbull Ave. Girard, OH 44420 P: 330-759-9834 x112 F: 330-759-8949 E: [email protected]<mailto:[email protected]> [cid:[email protected]]<http://www.firefoe.com/> From: Jamie Seidl <[email protected]> Sent: Wednesday, July 3, 2024 8:44 AM To: [email protected] Subject: [Sprinklerforum] FW: 2013 NFPA 14 7.5.3 Quick question on a holiday week. 7.5.3 states that "Where standpipes are interconnected at the top and bottom, check valves shall be installed at the base of each standpipe to prevent circulation". Is this requirement intended to apply to manual dry standpipes? NFPA 14 does not appear to make a distinction in this case, but if they're intended to prevent circulation, I would imagine that is not a concern with a manual dry system. Steve, are you on vacation yet? This one is up your alley. Thanks for your time. Jamie Seidl NICET SET #107472 Century Fire Protection<http://www.centuryfp.com/> | General Manager 3600 Woodpark Blvd. Suite G Charlotte, NC 28206 ___________________________________________________________________ p 704 888 3473 | m 704 650 0033 Facebook<https://www.facebook.com/CenturyFP> LinkedIn<https://www.linkedin.com/company/century-fire-protection> Twitter<https://twitter.com/centuryfp>