Mathew & Steve,

 

Thank you for the replies. I will make sure Mechanical Engineer is made
aware.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

                 CELL: (802) 373-0638  

              <mailto:[email protected]> [email protected]

 

From: [email protected] <[email protected]> 
Sent: Tuesday, June 25, 2024 1:29 PM
To: [email protected]
Subject: [Sprinklerforum] Re: Sprinkler Pipe passing through HVAC tin work

 

If the duct cannot be claimed to be supporting the pipe, and the temps are
within operational range, then I do not know of any reason it cannot be
done.

 

Was a party to it many, many years ago when I held a wrench. Have even cut a
hole or 2 previously and passed thu the duct.

 

R/
Matt

 

Matthew J. Willis, CWBSP, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721 C: (307) 236-8249

 <mailto:[email protected]> [email protected]

 

From: Tim Stone <[email protected] <mailto:[email protected]> > 
Sent: Tuesday, June 25, 2024 11:14 AM
To: sprinklerforum <[email protected]
<mailto:[email protected]> >
Subject: [Sprinklerforum] Sprinkler Pipe passing through HVAC tin work

 

Caution:  This email originated from outside of the organization.  DO NOT
click links or open attachments unless you recognize and trust the sender. 

  _____  

I have seen this many times where a Sprinkler Pipe passes thru duct work.
Primarily on existing older projects, Installed before I started designing
30 plus years ago.

Is this practiced allowed? I don't find any reference to it in NFPA 13. 

 

This just happened over the weekend when duct work came through a wall and
instead of offsetting down to get past an existing sprinkler branch line
pipe the duct maintained elevation and was installed around the pipe. 

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

                 CELL: (802) 373-0638  

              <mailto:[email protected]> [email protected]

 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to