Fantastic. That's what I ordered and wanted to double check.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Travis Mack <[email protected]>
Sent: Wednesday, May 22, 2024 8:39 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Interstitial Heads

It's been in the standards since the 2002 edition. Concealed combustible spaces 
with slope not exceeding 2:12 and <36" clear (paraphrasing) require specially 
listed sprinklers.

So yes, they have been required in those spaces for more than 20 years.


Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

________________________________
From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Wednesday, May 22, 2024 5:36:38 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Interstitial Heads


Is there a benefit, and or requirement, to use Interstitial heads instead of a 
plane jane 5.6k upright in those spaces?



Thank you,



Brian Harris, CET

BVS Systems Inc.

bvssystemsinc.com<http://bvssystemsinc.com/>

Phone: 704.896.9989

Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to