Since NFPA 13 (2002 edition) was published the sprinkler selected for protection of concealed combustible spaces less than 36” shall be listed for such use. An upright is not listed for that application.
Thank you. Brandon Telford Sent from my iPhone. On Wed, May 22, 2024 at 8:37 AM Brian Harris <[email protected]> wrote: > Is there a benefit, and or requirement, to use Interstitial heads instead > of a plane jane 5.6k upright in those spaces? > > > > Thank you, > > > > *Brian Harris, CET* > > BVS Systems Inc. > > bvssystemsinc.com > > Phone: 704.896.9989 > > Fax: 704.896.1935 > > > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected]