It’s been in the standards since the 2002 edition. Concealed combustible spaces 
with slope not exceeding 2:12 and <36" clear (paraphrasing) require specially 
listed sprinklers.

So yes, they have been required in those spaces for more than 20 years.


Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

________________________________
From: Brian Harris <[email protected]>
Sent: Wednesday, May 22, 2024 5:36:38 AM
To: [email protected] 
<[email protected]>
Subject: [Sprinklerforum] Interstitial Heads


Is there a benefit, and or requirement, to use Interstitial heads instead of a 
plane jane 5.6k upright in those spaces?