I'm not an IBC guy, but I don't think a 2-hour wall creates separate buildings 
in accordance with the model building code (2019 NFPA 14 section A7.10.1.2.3.1).

And if that door in the 2-hour wall is considered an exit opening of a 
horizontal exit, you may be required to provide additional hose connections 
there (section 7.3.2.2).

Ed Kramer


From: [email protected] <[email protected]>
Sent: Wednesday, April 3, 2024 8:43 AM
To: 'Discussion list on issues relating to automatic fire sprinklers' 
<[email protected]>
Subject: [Sprinklerforum] Standpipe Calculations

Asking this on behalf of Rowe Sprinkler Systems (Temporally Un-Retired)

We have a 4-story modular apartment building sprinklered in accordance with 
NFPA 13R with allowed exceptions, with 4 standpipes. The standpipes are 
connected at the 1st floor level. One each at the ends of the L shaped building 
and two at the approximate mid-point on either side of a 2-hour separation wall 
with self-closing, rated doors in the corridor.
The question is for purposes of calculating the standpipe can these be treated 
as two separate buildings? For example, 250 gpm at the far end of the 4th 
floor, 250 gpm at the far end of the 3rd floor and 250 gpm at the at the 
connecting point of the middle standpipe, for a total of 750 gpm.
Or do we have to calculate the additional standpipes up to 1250 gpm. Available 
water is the issue.


Richard L. Mote CET
Rimrock Design Services, LLC
Middleburg, PA 17842
Mobile 570-541-2685
EMAIL 
[email protected]<mailto:[email protected]>
WEB: www.rimrockdesignservicesllc.com

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to