Rated chase for sprinkler piping and/or riser appurtenances within a rated
stairway is excessive protection per past norms of practice.
I would tolerate sprinkler pipe and appurtenances in a stairway, provided
egress AND maintenance clearances.
Risk tolerance has declined over the years, but this ask might originate
from motivations that have not delinced over the years.

Scot Deal
Excelsior Risk & Fire Engineering
gms:  +420 606 872 129


The meaning of life is to find your gift.  The purpose of life is to give
it away - picasso




On Tue, Mar 26, 2024 at 3:48 PM Hinson, Ryan <[email protected]> wrote:

> Placement/coordination within the stairwell is also important since the
> riser location cannot encroach into the minimum egress width or height
> required through the stairwell.
>
>
>
> *Ryan L. Hinson**, PE*, SET***  \  Burns & McDonnell
>
> Associate Fire Protection Engineer \ Upper Midwest Region
>
> *O* 612-900-3755 \  *M* 763-688-4045 \  *F* 952-229-2923
>
> *[email protected] <[email protected]>*  \  burnsmcd.com
> <http://www.burnsmcd.com/>
>
> 8201 Norman Center Drive, Suite 500  \  Bloomington, MN 55437
>
> *Registered in: AK, LA, MD, MN, PA, TX, & UT
>
> **NICET IV - Water-Based Systems Layout
>
>
>
> *From:* Steve Leyton <[email protected]>
> *Sent:* Tuesday, March 26, 2024 3:57 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: Riser in a rated stair enclosure
>
>
>
> Of a separate riser ROOM for backflow, etc.   Definitely not saying that
> you need a chase within the stair shaft, just that you’re not allowed to
> use the under-landing space for a “riser room”.
>
>
>
> Steve
>
>
>
> *From:* Prahl, Craig <[email protected]>
> *Sent:* Tuesday, March 26, 2024 1:48 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: Riser in a rated stair enclosure
>
>
>
> I’ve never seen a requirement for a 1 or 2-hr enclosure of a riser in a
> stair.  The stair towers I’ve encountered are typically rated 2-hrs and the
> combination sprinkler/standpipe riser located under the first landing or
> off to the unused side of the ground level has never been rejected by an
> AHJ.
>
>
>
> Craig Prahl | Jacobs | Fire Protection SME – Special Hazards |
> [email protected] | www.jacobs.com
> <https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>
>
>
>
> *From:* Steve Leyton <[email protected]>
> *Sent:* Tuesday, March 26, 2024 4:30 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [EXTERNAL] [Sprinklerforum] Re: Riser in a rated stair
> enclosure
>
>
>
> Right, as long as your “riser/backflow room” is separated from the rest of
> the stair shaft.   And it might have to be 2-hour rated, not just 1-hour.
>
>
>
> To the question of the sprinkler riser, there isn’t any restriction in the
> code, except for the obvious provisions for fire-stopping penetrations.
>
>
>
> Steve L.
>
>
>
> *From:* Anthony Carrizosa <[email protected]>
> *Sent:* Tuesday, March 26, 2024 1:22 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: Riser in a rated stair enclosure
>
>
>
> We do backflows and risers in stairs all the time, typically below the
> intermediate landing, as long as it’s a minimum 1 hour construction then it
> has been ok with most jurisdictions. Remember standpipes and floor controls
> are typically in stairs as a standard.
>
>
>
> *Anthony Carrizosa *
>
> Project Manager *| *Fire Protection
>
> 7855 S 206th St Kent, WA 98032
>
> Cell: *206-679-5283* | Office Dir: *253-341-4593*
>
> https://archerconstruction.com
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2farcherconstruction.com*2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tHph3goA$>
>
>
>
> *From:* Jeff Werre <[email protected]>
> *Sent:* Tuesday, March 26, 2024 1:09 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Riser in a rated stair enclosure
>
>
>
> Does code allow a sprinkler riser to be installed in a rated stairwell?
>
>
>
> I cannot find anything that prohibits it, but would like others opinions
> (experiences).
>
>
>
> Thank you-
>
>
>
> *Jeff Werre, CFM  *
>
> *Fire Plan Review and Inspection Specialist*
>
>
>
> Development Services
>
> City of Goodyear, Arizona
>
> 1900 North Civic Square
>
> Goodyear, AZ 85395
>
>
>
> *c* 602 316-0704
>
>  *w* *goodyearaz.gov
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.goodyearaz.gov*2f&c=E,1,HWheNqpd4bMAObWDA1Pz4jKGCAJR-thfNkyG-V6ubIPnRmE78JXq5nU1kLB5Uv0b6yAs3DnR0fq9Cb648VwhZkjzd0drubjF-G192TGVad51Zbnsm7L6vOrmJg,,&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tVFDFq8g$>*
>
> *e* *[email protected] <[email protected]>*
>
>
>
>
>
>
>
>
>
>
>
> *From:* Ken Wagoner <[email protected]>
> *Sent:* Wednesday, February 21, 2024 1:17 PM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] Re: NFPA 14 2019 Hose Connection on the Roof
>
>
>
> *⚠** This email arrived from an external source - Please exercise caution
> when opening any attachments or clicking on links *
>
>
>
> Completely agree with you John.
>
> Considering that I work with two adjacent agencies, each of which uses a
> different hose thread.  One uses National Standard Thread, the other
> National Hose Thread.  It's difficult to explain to contractors that
> identification of the hose threads to be supplied on private fire hydrants
> or hose valves can be as critical as it gets.
>
> sincerely,
>
> *Ken Wagoner, SET*
> *Parsley Consulting*
>
> * 500 West Mechanic Street Harrisonville, Missouri 64701-2235*
> *Phone: (760) 745-6181 *
> *Visit the website
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tX2yXVSk$>*
>
>
>
> On 2/21/2024 1:13 PM, John Denhardt wrote:
>
> Rick’s and Steve’s comments are spot on. Give the fire department what
> they need/want. Do not install something that no one will ever use in an
> emergency condition.
>
>
>
> John
>
> John August Denhardt, P.E.
>
> Vice-President Engineering and Technical Services
>
> American Fire Sprinkler Association
>
> 301-343-1457
>
>
>
> On Feb 21, 2024, at 13:30, Rick Matsuda <[email protected]>
> <[email protected]> wrote:
>
> 
>
> Steve’s guidance is the best.
>
> When it comes to hose valves and standpipe requirements, always verify
> with the AHJ to find out what they want.
>
> Rick
>
>
>
> On Feb 21, 2024, at 12:09 PM, Steve Leyton <[email protected]>
> <[email protected]> wrote:
>
> 
>
> To Rick’s comments:
>
> Concur, and also offer that while the standard doesn’t require a valve
> where there is no roof access, I am aware of numerous AHJ’s who do.   The
> stated intent of the rooftop connection(s) is to enable forward flow
> testing of the system.   However – and this goes to my mantra of many years
> now – it is incumbent on the designer to verify with the serving FD is they
> require roof connections that they may use for firefighting.   I have been
> made aware of several fire incidents that used roof connection hose streams
>  and I am also aware of fireground strategies that encompass these
> connections.
>
>
>
> The foregoing is my opinion only and does not represent NFPA or the NFPA
> 14 Technical Committee, nor intended to serve as an interpretation of the
> standard.
>
>
>
> Steve L.
>
>
>
>
>
>
>
> *From:* Rick Matsuda <[email protected]> <[email protected]>
> *Sent:* Wednesday, February 21, 2024 9:51 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers
> <[email protected]>
> <[email protected]>
> *Subject:* [Sprinklerforum] Re: NFPA 14 2019 Hose Connection on the Roof
>
>
>
> This is my opinion only from what I remember after being retired for ten
> years.
>
>
>
> The requirement for installing a hose valve is driven by the stairway
> requirements found in the building code which requires at least one
> stairway providing access to the roof.
>
>
>
> If the stairway extends to the roof, then a hose valve is required at the
> top landing or on the roof.
>
>
>
> If there is no roof access from the stairway, then no hose valve is
> required.
>
>
>
> The fire service will use the hose valve where they have safe access from
> the stairway but they will not walk across the roof dragging fire hose to
> hook up to a hose valve located where no safe access was provided.
>
> Rick Matsuda
>
>
>
> On Feb 21, 2024, at 10:47 AM, Fpdcdesign <[email protected]> wrote:
>
> 
>
> There are people here with more experience than I,  but if one outlet goes
> to the roof, the requirement is met.
>
>
>
>
>
> On Feb 21, 2024 at 11:34 AM, <Joe Burtell [MT-BILL]
> <[email protected]>> wrote:
>
> If I have 3 stair towers and the middle on has access to the roof and I
> provide a connection as required by 7.3.2.7* “Hose connections shall be
> provided at the highest landing of stairways with stairway access to a
> roof”, do the other (2) not have to go to the roof because of 7.3.2.9.2
> “The hose connection required by 7.3.2.9 shall not be required where at
> least one hose connection in accordance with 7.3.2.7 is provided in the
> building”.
>
>
>
> <image001.jpg>
>
> *Joe*
>
>
>
> *Burtell*
>
> Fire Sprinkler Manager
>
> *D*
>
> *C*
>
>
>
>
>
> 406-204-4653
>
> 406-861-4507
>
> 3004 1st Ave South
>
> Billings
>
> ,
>
> MT
>
>  59101
>
> Office:
>
> 406‑652‑7697
>
> www.summitfiresecurity.com
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.summitfiresecurity.com*2f&c=E,1,ZyzzqWo58xliyC5jRd9RdTLBBZo5jBEbiHix11FarpdW6p9BZLi5cyYnCyfcGhCFs7Mjew4A84L4gMd9Zn-QcKk5wbpkUpp2_prGEtUdqFeTwliA1vO3eEu-2E71&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tjGXKPfo$>
>
> This information transmitted, including attachments, is intended only for
> the person(s) or entity to which it is addressed and may contain
> confidential and/or privileged material. Any review, retransmission,
> dissemination or other use of, or taking of any action in reliance upon
> this information by persons or entities other than the intended recipient
> is prohibited. If you received this in error, please contact the sender and
> destroy any copies of this information.
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,zSczA6fh1z_DZmRiDK-SmOo2Q4iD1ybs-dofDAvbol2ARplwrC3CBPuJ5a3M1J8_FALzCrYwXVIdMdoRY1GetEF5HPRcSwVLnkfeGB7fJAT0jA,,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tFELFh_8$>
> To unsubscribe send an email to
> [email protected]
>
> <image001.jpg>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,cn2QOu3An6_NJyh_-n31_xLLKLAryTT4kv8MVY8TqJ2tAbIic9WRP3VMiL7Zsa_JQjzaIzYp9C1xb376t1oQxX-odSiNENfy2M5txOLU23NwBAyI53R1EyIXksgS&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tXyO6WrE$>
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,Gi862oLoF3I3PplbXyhBlyIqWk1hlUfaFq9LFqSSetXU_-QR2vszIPHoPCLemLpvP0IDslPxYZ0DJomXGuGZ1wGFfIq8RBojUhao19aiCM1LBGtLKy2trXyxLJY,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tEoX6sD4$>
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,MWR4WxvMm_voDTNku1D03F-6A9h7Gjbw2wvOS49dDZ4dGxceCjdtDa2_nTMSn1oskjiBgoFgJqtSxtjY9p-j1EVkWm8Y_tlvE_y1U995rCMZ_84,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3twlbc8x8$>
> To unsubscribe send an email to
> [email protected]
>
>
>
>
>
> _________________________________________________________
>
> SprinklerForum mailing list:
>
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> <https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,Zpm0EABfFsWYaANMGgf1uWLhtVfyI7HnZMUfAbuYLjv9MsLHX1mMcjxoSR48b1-eE-_y1osOjMNHzemMmoczBd_hkPjZgDRcLqK2w6x0YKgX&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3ttg6vig4$>
>
> To unsubscribe send an email to [email protected]
>
>
>
> All messages created in this system belong to the City of Goodyear and
> should be considered a public record subject to disclosure under Arizona
> Public Records Law (A.R.S. 39-121). City employees, City public officials,
> and those who generate E-mail to them, should have no expectation of
> privacy related to the use of this technology. If you are not the intended
> recipient you are notified that disclosing, copying, distributing or taking
> any action in reliance on the contents of this information is strictly
> prohibited.
>
>
> ------------------------------
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to