I worked on a project where we required to install a roof manifold on a roof 
of a wood frame building with a 1:12 pitch. The manifold was 1/2 the length of 
the building from the roof access, which itself was sketchy. The FD claimed 
they would use it in a fire. I would not want    be up 4 floors in that burning 
bldg.   
  
  
  
  
  
  
  

  
  
>   
> On Feb 21, 2024 at 4:05 PM,  <Dwight Havens (mailto:[email protected])>  
> wrote:
>   
>   
>   
>   
>
>   
> And don't set the fire department up for failure.
>   
>
>     
>   
>   
> On Wednesday, February 21, 2024 at 02:14:09 PM EST, John Denhardt  
> <[email protected]>  wrote:
>   
>
>   
>
>   
>   
>   
> Rick’s and Steve’s comments are spot on. Give the fire department what they 
> need/want. Do not install something that no one will ever use in an emergency 
> condition.     
>
>   
> John
>   
>   
> John August Denhardt, P.E.  
> Vice-President Engineering and Technical Services
>   
> American Fire Sprinkler Association   
>   
> 301-343-1457
>   
>   
>
>   
> > On Feb 21, 2024, at 13:30, Rick Matsuda  <[email protected]>  wrote:
> >   
>     
> >   
> > 
> >   
>   
>   
>   
>   
>
>   
> Steve’s guidance is the best.   
>   
> When it comes to hose valves and standpipe requirements, always verify with 
> the AHJ to find out what they want.   
>   
> Rick
>   
>
>   
> > On Feb 21, 2024, at 12:09 PM, Steve Leyton  <[email protected]>  
> > wrote:
> >   
>     
> >   
> > 
> >   
>   
>   
>   
>   
>
> To Rick’s comments:
>   
>  Concur, and also offer that while the standard doesn’t require a valve where 
> there is no roof access, I am aware of numerous AHJ’s who do.      The stated 
> intent of the rooftop connection(s) is to enable forward flow testing of the 
> system.      However – and this goes to my mantra of many years now – it is 
> incumbent on the designer to verify with the serving FD is they require roof 
> connections that they may use for firefighting.      I have been made aware 
> of several fire incidents that used roof connection hose streams    and I am 
> also aware of fireground strategies that encompass these connections.     
>
>   
>
>   
>
>   
>
> The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
> Technical Committee, nor intended to serve as an interpretation of the 
> standard.
>
>   
>
>   
>
>   
>
> Steve L.
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
> From:  Rick Matsuda  <[email protected]>
>   Sent:  Wednesday, February 21, 2024 9:51 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected]>
>   Subject:  [Sprinklerforum] Re: NFPA 14 2019 Hose Connection on the Roof
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> This is my opinion only from what I remember after being retired for ten 
> years.   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> The requirement for installing a hose valve is driven by the stairway 
> requirements found in the building code which requires at least one stairway 
> providing access to the roof.   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> If the stairway extends to the roof, then a hose valve is required at the top 
> landing or on the roof.   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> If there is no roof access from the stairway, then no hose valve is required. 
>   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> The fire service will use the hose valve where they have safe access from the 
> stairway but they will not walk across the roof dragging fire hose to hook up 
> to a hose valve located where no safe access was provided.   
>
>   
>   
>   
>
> Rick Matsuda   
>
>   
>   
>   
>   
>
>
>   
>
>
>   
> >   
> >
> > On Feb 21, 2024, at 10:47 AM, Fpdcdesign  <[email protected] 
> > (mailto:[email protected])>  wrote:
> >
> >   
>   
>   
> >   
> >   
> >
> > 
> >
> >   
> >   
> >
> > There are people here with more experience than I,    but if one outlet 
> > goes to the roof, the requirement is met.   
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> >
> >   
> >   
> >
> >
> >   
> > >   
> > >   
> > >
> > > On Feb 21, 2024 at 11:34 AM,  <Joe Burtell [MT-BILL] 
> > > (mailto:[email protected])>  wrote:
> > >
> > >   
> > >   
> > >   
> > >
> > > If I have 3 stair towers and the middle on has access to the roof and I 
> > > provide a connection as required by 7.3.2.7* “Hose connections shall be 
> > > provided at the highest landing of stairways with stairway access to a 
> > > roof”, do the other (2) not have to go to the roof because of 7.3.2.9.2 
> > > “The hose connection required by 7.3.2.9 shall not be required where at 
> > > least one hose connection in accordance with 7.3.2.7 is provided in the 
> > > building”.
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > >
> > >
> > >   
> > > <image001.jpg>
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > Joe​​​​
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > Burtell
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > Fire   Sprinkler   Manager
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > D
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > C
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > 406-204-4653
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > 406-861-4507
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > 3004   1st   Ave   South
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > Billings
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > ,   
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > MT
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > >   59101
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > Office:   
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > 406‑652‑7697
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > www.summitfiresecurity.com 
> > > (https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.summitfiresecurity.com%2F&data=05%7C02%7Cjdenhardt%40stricklandfire.com%7C5250e29a92054c3c62ea08dc330b2b03%7Cd658cbf30820420e8485ef2e373e8459%7C0%7C0%7C638441370299820330%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C&sdata=gNjGuFJg4Teq%2BJjvDwu8nRaY%2F56qV6EGnwa1D1DdL4I%3D&reserved=0)
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > This information transmitted, including attachments, is intended only for 
> > > the person(s) or entity to which it is addressed and may contain 
> > > confidential and/or privileged material. Any review, retransmission, 
> > > dissemination or other use of, or taking of any action in reliance upon 
> > > this information by persons or entities other than the intended recipient 
> > > is prohibited. If you received this in error, please contact the sender 
> > > and destroy any copies of this information.
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > > _________________________________________________________ SprinklerForum 
> > > mailing list:  
> > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > >  
> > > (https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Flists.firesprinkler.org%2Flist%2Fsprinklerforum.lists.firesprinkler.org&data=05%7C02%7Cjdenhardt%40stricklandfire.com%7C5250e29a92054c3c62ea08dc330b2b03%7Cd658cbf30820420e8485ef2e373e8459%7C0%7C0%7C638441370299830523%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C&sdata=6%2FoOk5ahuP%2BbE3Z39HnA9n0becj5E869Q4nXEEtmboI%3D&reserved=0)
> > >   To unsubscribe send an email to  
> > > [email protected] 
> > > (mailto:[email protected])
> > >
> > >   
> > >   
> >   
> >   
> >   
> >
> >
> >
> >   
> > <image001.jpg>
> >     
> >
> >  _________________________________________________________
> >  SprinklerForum mailing list:
> >   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> > (https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Flists.firesprinkler.org%2Flist%2Fsprinklerforum.lists.firesprinkler.org&data=05%7C02%7Cjdenhardt%40stricklandfire.com%7C5250e29a92054c3c62ea08dc330b2b03%7Cd658cbf30820420e8485ef2e373e8459%7C0%7C0%7C638441370299837265%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C&sdata=bkmJrRZp0F3C%2BYVstj8YvsinbDFHDwg0N1R3e5jW9TE%3D&reserved=0)
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])   
> >
> >   
> >   
> >
> >   
>   
>
>   
>   
>
>   _________________________________________________________
>   SprinklerForum mailing list:
>   https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>   To unsubscribe send an email to [email protected]
>   _________________________________________________________
>   SprinklerForum mailing list:
>   https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>   To unsubscribe send an email to 
> [email protected]       
>   
>  _________________________________________________________
>  SprinklerForum mailing list:
>   https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>  To unsubscribe send an email to  
> [email protected] 
> (mailto:[email protected])        
> _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to