The building code and NFPA 14 both state that where required, standpipe hose 
connections shall be installed on every floor level landing of every required 
exit stair.  There are obviously additional considerations, such as whether the 
local FD prefers connections on intermediate landings instead of floor level, 
or if a stair goes to the roof or not.  In this case, you’ve ID’d a condition 
where there’s no access to the first floor from the stairs (if I’m 
understanding correctly), so there’s not any value to the FD if valves are 
located there.

Some FD’s will waive hose connections on the level of apparatus access as they 
can pull attack lines directly into the building from their pumper.   Some FD’s 
may want a valve or valves in another location on that ground floor.   Bottom 
line is (broken record here) that you should consult with the responding FD to 
place the valve or valves in a location that they approve and for which they 
can pre-plan and ultimately, use the valve as safely and effectively as 
possible.


The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Protection Design and Consulting
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training







From: Fpdcdesign <[email protected]>
Sent: Wednesday, March 27, 2024 7:40 AM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Main floor hose valve location.

I am working on a small 4 story building where we are required to install a 
standpipe (as well as a full 13 sprinkler system). The first floor consists of 
a conference area, office space and various mechanical and storage rooms. The 
conference space and office area have direct access to the outside, but there 
is no communicating space between them. The 2 stairways lead to an outside 
access only. The elevator lobby has an outside door but does not connect to the 
stairways or conference and office spaces. The total footprint of the building 
is less than 3000 sqft.

Where do you put the hose valve on the 1st floor?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)