Well summed up Ken..

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>

From: Ken Wagoner <[email protected]>
Sent: Thursday, March 14, 2024 2:07 PM
To: [email protected]
Subject: [Sprinklerforum] Re: Gang drain crossing seismic joint

Steve,

three points here.

  *   §18.4.1 requires clearance for a drain extending through a wall, floor, 
platform, foundations.

  *   §18.5.1.6 omits any bracing requirements for drain piping downstream of 
the drain valve.

  *   It isn't a branch line so restraint is not required. §18.6.4

All references from the 2022 edition of -13.

So my thought is that if you have the required clearance when your piping 
crosses the seismic joint, nothing further is needed.

This is my opinion only.
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued 
pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of 
the author and does not necessarily represent the official position of the NFPA 
or its Technical Committees. In addition, this correspondence is neither 
intended, nor should it be relied upon, to provide professional consultation or 
services. It should be noted that the above is my opinion as a member of the 
NFPA Automatic Sprinkler System Hanging and Bracing Committee and the Hanging 
and Bracing for Fire Suppression Systems Committee in accordance with the NFPA 
Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the NFPA or its 
Committees


On 3/14/2024 2:35 PM, Steve Leyton wrote:
All (especially Californicators):

We have to cross a seismic joint with the piping that supplies a combination 
standpipe in a mid-rise building (no PRV’s to test).   As a combo, there’s a 
collection pipe for sectional test and drain discharge, and for reasons 
peculiar to this building, our first choice is to bring the gang drain back to 
the riser room, as it’s the only place with a SS trap in the basement.   We’re 
trying to decide whether a seismic joint is required of the drain pipe, which 
is normally dry and never under system pressure in any case.   I reckon I 
should know this, but I don’t think we’ve had to address this condition in 
forever, maybe never.


[cid:[email protected]]
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.protectiondesign.com%2f&c=E,1,oeBy0qhzYU9iI9fuhud9CT-BY8AEDWVkYf20OsfIbt7-fe5gGmgLH0dWPU7wVK9CDK90ENWZtafNL1qQpofRh9TK4ukNtBCGScw6zCq-_ngl0vpG&typo=1>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training






_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,gJxL-f6jSDW1_FWvypDzGRMuxNV4xObyXtOnrgAEtoGpUA1VGziy2ypQrG24N6I4WZKDpOFXpSYDWMSGNSRqH9kXfRHKXWqIJA_iFHuSuUhkucmY&typo=1>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to