I would say that drain piping downstream of the valve is not required to be 
braced.  One of the things I like to impress upon people when teaching seismic 
is that you brace and secure the pipe to keep the water in the piping.  It is 
also to insure that piping required for the operation of the system shall 
retain water to keep it functional.  Since a gang drain is downstream of the 
drain valve and has no bearing on the functionality of the system in the event 
sprinklers or standpipe were ever activated, then I would say it is not 
required.


Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348
Email: [email protected]

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Steve Leyton <[email protected]>
Sent: Thursday, March 14, 2024 12:35 PM
To: [email protected]
Subject: [Sprinklerforum] Gang drain crossing seismic joint

All (especially Californicators):

We have to cross a seismic joint with the piping that supplies a combination 
standpipe in a mid-rise building (no PRV's to test).   As a combo, there's a 
collection pipe for sectional test and drain discharge, and for reasons 
peculiar to this building, our first choice is to bring the gang drain back to 
the riser room, as it's the only place with a SS trap in the basement.   We're 
trying to decide whether a seismic joint is required of the drain pipe, which 
is normally dry and never under system pressure in any case.   I reckon I 
should know this, but I don't think we've had to address this condition in 
forever, maybe never.


[cid:[email protected]]
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to