I would hope there would be a provision that if you hydraulicly prove it whit 
one connection that should be acceptable.

Christopher S. Wilson SET
Project Design Manager
Treasure Valley Fire Protection
2731 S. Saturn Way
Boise, ID 83709
Phone:  208-362-1888
Fax: 208-362-2207

please note all TVFP email
addresses have changed
new email below

[email protected]<mailto:[email protected]>

From: Steve Leyton <[email protected]>
Sent: Thursday, March 14, 2024 10:48 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Cc: Dewayne Martinez <[email protected]>
Subject: [Sprinklerforum] Re: FDC for Standpipe

That’s hydraulics.  If you can deliver the demand with no more inlet pressure 
than the FD is willing to accept, I think you can use 4” for the FDC.


The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Protection Design and Consulting
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training







From: Dewayne Martinez 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, March 14, 2024 9:30 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Cc: Dewayne Martinez 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: FDC for Standpipe

Would a 5”x4” Storz be 750gpm because of the Storz connection size or 500gpm 
because of the pipe?

From: John Denhardt 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, March 14, 2024 10:39 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: FDC for Standpipe

Here is the reference:
NFPA 14 - 2024
10.7.3.1.1

Where a 4 in. (100 mm) inlet is used, the assumed flow per inlet shall be 500 
gpm (1900 L/min).
10.7.3.1.2

Where a 5 in. (125 mm) inlet is used, the assumed flow per inlet shall be 750 
gpm (2850 L/min).

The above is my opinion and has not been processed as a formal interpretation 
in accordance with the NFPA Regulations Governing Committee Projects. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the AFSA, and/or NFPA or its technical committees.AFSA cannot 
provide design or consulting engineering services, and this opinion should 
therefore not be considered, nor relied upon, as such.

Thanks,
John

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
John August Denhardt, PE
Vice President, Engineering and Technical Services
American Fire Sprinkler Association
m: p:
301-343-1457
214-349-5965 ext 121
w:
firesprinkler.org<https://link.edgepilot.com/s/05225bcc/ClJhZiur_EuTVK5AEN1N7A?u=http://firesprinkler.org/>


Treat Your Apprentices Like VIPs!
AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that comes 
straight from our expert instructors. They lead the way to ensure your men and 
women are trained, letting you focus on OJT. Click 
here<https://link.edgepilot.com/s/0d0f910e/I3IXFpacwkKPqQT68TdoAA?u=https://www.firesprinkler.org/sprinkler-apprentice-training/>
 to learn more and enroll.


On Thu, Mar 14, 2024 at 11:25 AM John Denhardt 
<[email protected]<mailto:[email protected]>> wrote:
To all - review NFPA 14 -2024 as it has new requirements for 4" and 5" storz 
connections.
4" is limited to 500 GPM per connection
5" is limited to 750 GPM per connection

Unfortunately, I'm at a conference where my internet connection is very 
limited, otherwise I would give you a section reference.


The above is my opinion and has not been processed as a formal interpretation 
in accordance with the NFPA Regulations Governing Committee Projects. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the AFSA, and/or NFPA or its technical committees.AFSA cannot 
provide design or consulting engineering services, and this opinion should 
therefore not be considered, nor relied upon, as such.

Thanks,
John

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
John August Denhardt, PE
Vice President, Engineering and Technical Services
American Fire Sprinkler Association
m: p:
301-343-1457
214-349-5965 ext 121
w:
firesprinkler.org<https://link.edgepilot.com/s/05225bcc/ClJhZiur_EuTVK5AEN1N7A?u=http://firesprinkler.org/>


Treat Your Apprentices Like VIPs!
AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that comes 
straight from our expert instructors. They lead the way to ensure your men and 
women are trained, letting you focus on OJT. Click 
here<https://link.edgepilot.com/s/0d0f910e/I3IXFpacwkKPqQT68TdoAA?u=https://www.firesprinkler.org/sprinkler-apprentice-training/>
 to learn more and enroll.


On Thu, Mar 14, 2024 at 11:09 AM Ken Wagoner 
<[email protected]<mailto:[email protected]>> wrote:
Brian,

Yes, I have been required to provide such a connection in the past.  It has 
been rare, and it was a gorilla sized high rise building.

For me arguing with the AHJ over this seemed pointless.

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://link.edgepilot.com/s/dde5c241/bF3XlLWBtU65V9CSGGAr2A?u=https://linkprotect.cudasvc.com/url?a=http%253a%252f%252fwww.parsleyconsulting.com%252f%26c=E%2C1%2CY5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK%26typo=1>


On 3/14/2024 10:01 AM, Brian Harris wrote:
Anybody ever had an AHJ required a 4-way FDC with (4) Storz connections to feed 
a standpipe? I get the (1) 2-1/2” connection per 250 gpm but you’re also 
allowed a “large diameter” hose connection. In this case the current FDC is a 
5” Storz on 6” underground.

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://link.edgepilot.com/s/c471525e/x4UtYt2Sbk2diYD-cOmpjg?u=http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935



_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://link.edgepilot.com/s/eb95be2f/xJ_tzfhPPESks3df1GbOsw?u=https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://link.edgepilot.com/s/eb95be2f/xJ_tzfhPPESks3df1GbOsw?u=https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to