Here is the reference: NFPA 14 - 2024 10.7.3.1.1 Where a 4 in. (100 mm) inlet is used, the assumed flow per inlet shall be 500 gpm (1900 L/min). 10.7.3.1.2
Where a 5 in. (125 mm) inlet is used, the assumed flow per inlet shall be 750 gpm (2850 L/min). *The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the **AFSA, and/or NFPA or its technical committees.**AFSA cannot provide design or consulting engineering services, and this opinion should therefore not be considered, nor relied upon, as such.* Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org *Treat Your Apprentices Like VIPs!* AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that comes straight from our expert instructors. They lead the way to ensure your men and women are trained, letting you focus on OJT. Click here <https://www.firesprinkler.org/sprinkler-apprentice-training/> to learn more and enroll. On Thu, Mar 14, 2024 at 11:25 AM John Denhardt <[email protected]> wrote: > To all - review NFPA 14 -2024 as it has new requirements for 4" and 5" > storz connections. > 4" is limited to 500 GPM per connection > 5" is limited to 750 GPM per connection > > Unfortunately, I'm at a conference where my internet connection is very > limited, otherwise I would give you a section reference. > > > *The above is my opinion and has not been processed as a formal > interpretation in accordance with the NFPA Regulations Governing Committee > Projects. This is provided with the understanding that the AFSA assumes no > liability for this opinion or actions taken on it and they are not to be > considered the official position of the **AFSA, and/or NFPA or its > technical committees.**AFSA cannot provide design or consulting > engineering services, and this opinion should therefore not be considered, > nor relied upon, as such.* > > > Thanks, > John > > John August Denhardt, PE > *Vice President, Engineering and Technical Services* > > *American Fire Sprinkler Association* > m: p: 301-343-1457 > 214-349-5965 ext 121 > w: firesprinkler.org > > > > *Treat Your Apprentices Like VIPs!* > AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that > comes straight from our expert instructors. They lead the way to ensure > your men and women are trained, letting you focus on OJT. Click here > <https://www.firesprinkler.org/sprinkler-apprentice-training/> to learn > more and enroll. > > > On Thu, Mar 14, 2024 at 11:09 AM Ken Wagoner <[email protected]> > wrote: > >> Brian, >> >> Yes, I have been required to provide such a connection in the past. It >> has been rare, and it was a gorilla sized high rise building. >> >> For me arguing with the AHJ over this seemed pointless. >> >> sincerely, >> *Ken Wagoner, SET* >> >> >> *Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri >> 64701-2235* >> *Phone: (760) 745-6181 * >> *Visit the website >> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>* >> >> >> On 3/14/2024 10:01 AM, Brian Harris wrote: >> >> Anybody ever had an AHJ required a 4-way FDC with (4) Storz connections >> to feed a standpipe? I get the (1) 2-1/2” connection per 250 gpm but you’re >> also allowed a “large diameter” hose connection. In this case the current >> FDC is a 5” Storz on 6” underground. >> >> >> >> Thank you, >> >> >> >> *Brian Harris, CET* >> >> BVS Systems Inc. >> >> bvssystemsinc.com >> >> Phone: 704.896.9989 >> >> Fax: 704.896.1935 >> >> >> >> _________________________________________________________ >> SprinklerForum mailing >> list:https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org >> To unsubscribe send an email to [email protected] >> >> >> >> _________________________________________________________ >> SprinklerForum mailing list: >> >> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org >> To unsubscribe send an email to >> [email protected] > >
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]
